Which Part of Specification Takes Precedence?

6/25/2021

7 Comments

 
A typical specification is broken down into 3 parts:
Part 1 – General
Part 2 – Products
Part 3 – Execution

In a typical specification for sprinkler pipe we often see something like this:
Part 2 - Products
2.2 Steel Pipe and Fittings
Schedule 40 Galvanized and Black steel pipe
Schedule 10 Black steel in pipe NPS 2.5 and larger

Part 3 - Execution
3.12 Piping Schedule
NPS 2 and smaller - Schedule 40 black steel
NPS 2-1/2 and larger - Schedule 40 black steel

When Part 2 and Part 3 of the same spec contradict one another, which part rules?

I know the answer is to write an RFI, but we often don’t get an answer prior to bid time.

Also, what is the thought process of the EOR for providing a spec like this in a bid document to begin with?

​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe​
7 Comments
schulman
6/25/2021 08:08:40 am

The EOR made an error ... he's not TRYING to confuse you.
Our documents include a statement that requires you bid the more expensive and/or more detailed in the case of discrepancies. You should check to see if the documents have a statement like this.
Also - having made this mistake several times before, I know that most contractors will go low to win the bid, then call me and ask for permission to do the 2-1/2" piping and larger as Schedule 10 ...
I usually allow it.
Good Luck.

Reply
Jon Sullivan
6/25/2021 08:10:35 am

You'll have to see the front-end specification, but typically the most restrictive applies. There's a really good design spec article on this site, but typically it rounds out the drawings and gives you more detail than "per NFPA 13".

I'd ask the RFI so everyone is bidding the same.

Reply
Brad K
6/25/2021 08:13:11 am

When time is of the essence and you believe an RFI will not be answered, bid the competitive priced option. Then make written exception to the contradicting spec portion in your proposal.
Otherwise my gut is to comply with Execution over Products if I had to pick one or the other.

Reply
CJ Bonczyk
6/25/2021 09:39:08 am

9 out of 10 times you are to comply with the execution section of the specifications. Many times the other sections are boilerplate and just copy and pasted from similar jobs. It is best to try and RFI on the front end and see which option the specifying engineer desires, because you can provide some VE options that may be better overall for cost, installation, maintenance, performance, etc. When bidding clarify exactly what you are providing where there is contradicting information in the specifications and you don't have time to RFI the information.

Reply
Dave Branson
6/25/2021 12:22:21 pm

The specification example you showed does not have a conflict. Often under PRODUCTS items are grouped together - in this case Schedule 40 Galvanized and Black Steel Pipe. EXECUTION delineates between use cases, as per this example.

Reply
Greg Stoner
6/28/2021 07:44:53 am

Why list a product in section 2, i.e. 2-1/2" and larger black schedule 10, if the product is not allowed?

Reply
Dave Branson
6/28/2021 08:33:59 am

“Products” covers all portions of the project unless stated otherwise - one would typically define usage in the “Execution” section, but if needed one could further segregate piping by materials within the “Products” section.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT