When hose allowance is added to the sprinkler demand on a Class III Standpipe/Sprinkler wet riser, where on the system are the inside and outside flow and pressure allowances input when calculating the system?
NFPA 13 Chapter 19 states that the allowances are not required when calculating a combined system, which appears to contradict NFPA 14 requirements to include them. In my case, the sprinkler demand is for OH2 (ceiling higher than 40 ft), resulting in a sprinkler demand plus hose allowance that is greater than the standpipe demand. If I don’t include hose allowance in the sprinkler calculation as per Chapter 19, this combined system is not equivalent and robust as two independent systems. Any thoughts? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Glenn Berger
4/30/2026 08:22:03 am
The NFPA 13 calculations requires adding its version of hose allowance into the system at various points at the discretion of the system designer/engineer.
Reply
Michael Tapuska
4/30/2026 10:56:41 am
In my case NFPA 13 is a more onerous flow requirement than NFPA 14.
Reply
Dan Wilder
4/30/2026 08:55:01 am
So NFPA 13 - 2022
Reply