Where in Code is a Permit Required to be Pulled?

5/14/2024

12 Comments

 
Are there any universal, non-AHJ-specific requirements for permitting sprinkler alterations and/or repairs?

I have been told that “code” requires a permit to be pulled for any and all sprinkler alterations. Upon further questioning, I determined that this came from a fire marshal showing my colleague something in the IBC once, but, even if that were true, wouldn’t that still require adoption and implementation by a jurisdiction?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
5/14/2024 07:57:11 am

IBC/IFC Chapter 1, Sections 101, 102, 103, 105, 105 (**Permits**), 107, 109, 110, 111, 114, 115, 116 for example.

As building codes (IBC/NFPA 5000 along with other referenced bodies), are voted on (with or without amendments) and approved through the legislature, they become lawful, enforceable, and with means to penalize parties that violate them.

Reply
Mike Bauer
5/14/2024 08:17:40 am

Section 105.7.1 of the International Fire Code States "A construction permit is required for installation of or modification to an automatic fire-extinguishing system. Maintenance preformed in accordance with this code is not considered to be a modification and does not require a permit".

I can only speak for my area, but all Jurisdictions here have adopted by Ordinance an edition of the Fire Code, be it ICC or NFPA. That adopted document is what we have authority to enforce.

Reply
Craig Hanson link
5/14/2024 08:38:54 am

This is a good question! Lots of designers, installers and just everyday people do not realize the role the International Building Codes (IBC, IFC, IMC etc.)have in interaction with the NFPA's. If a state has adopted the IBC then it is part of the state laws and regulations. This means that the "Code" is the IBC/IFC and everything else is a "Standard" that is referenced. You do not apply any portion of a NFPA unless it is referenced in the IBC/IFC (Chapter 80). for instance the NFPA 13R does not specifically reference balconies in an apartment building but the IFC does and as such, the requirements of the IFC take priority as the code. This gets really tricky when dealing with FM standards. FM is not referenced in the IFC and as such is not pat of the code or the standard. FM data sheets are outside the scope of the NFPA 13. Technically they can be allowed as Alternative Means and Method but needs approval from the AHHJ to use them. I hope this helps.

Reply
Brett
5/14/2024 08:42:25 am

NFPA 1 has a section for permits.
NFPA 1:1.12 Permits and Approvals.
Within the section is a table listing all of the times a permit is required. NFPA 1:1.12.8 Permits shall be required in accordance with Table 1.12.8(a) through Table 1.12.8(d).

Reply
JH
5/14/2024 01:39:44 pm

Came here to echo Brett and add:

In Florida, it is mandatory per State Statute for all jurisdictions to adopt the Florida Fire Prevention Code (ie: NFPA 1&101) as a minimum code.
Check your State and local LDCs / Municipal codes to see which Code has been adopted into law in your jurisdiction.

Reply
Jesse
5/14/2024 08:47:20 am

NFPA, IBC and its sub-iterations are inherently NOT law or ordinance. They have to be adopted by a governing body i.e. city council, county council, state legislature, etc.

In rural places where building codes don't apply, there may not be a permit requirement/ I've run into that a few times and in those cases run my plans through the State Fire Marshal's Office here in Texas for courtesy review.

However, and this is really important information I learned long ago: All of NFPA and all of IBC is considered a consensus standard. And even though it may not be strictly "code" in some of those rural areas, it is admissible in court as a national consensus standard.

Reply
Craig Hanson link
5/14/2024 09:07:06 am

That is not entirely true throughout the nation. Some states, such as Washington, has the adoption of the IBC in the WAC (Washington Administrative Code) other states like California it is under Title 24 of the California Code of Regulations. Some states leave it up to the individual AHJ's.

Reply
Jack G
5/14/2024 08:56:57 am

Its in IBC.

However, why would you not want to pull a permit, have an iinspection? Money?
Everytbing should go thru a ped.itting process.
For ljabilities sake.

Reply
Anthony
5/14/2024 09:06:51 am

There is no requirement per IBC or NFPA code to obtain a permit to begin work. That is left up to the locality. Gov't selects the codes to follow and adds fees to review plans.

Reply
sean
5/14/2024 10:07:04 pm

please reread the permits section in the ifc or ibc

Reply
James Art, FPE
5/15/2024 02:50:12 pm

Some owners, like the gov't are not subject to local or state inspection.
I investigated a big fire in a 100 x 100 foot addition to a Post Office distribution warehouse in Richmond, Ca.

The addition burned to the ground, and burned 5 rows of sprinklers into the attached building.

No AHJ, no local permits?:
It was 40 foot high rack storage, but sprinklered to Ord Haz.

The riser was still standing, even tho the sheet metal warehouse was gone, but there had never been any wires connected to the water flow or valve tamper switches, even tho the addition was 10 years old. There were other shortcomings as well.

If they had had a Building or Fire Dept. inspection, or an FPE, hopefully the outcome would have been different.

Many agencies, esp. the government and the military, are "self insured", which can mean UnInsured, so they don't even have an insurance co. inspection.

Reply
sean
5/15/2024 08:02:10 pm

does the GSA not cover the post office?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT