When to Modify CMDA in a New System Design?

4/10/2026

3 Comments

 
I am doing CMDA overhead sprinklers for in-rack class 4 storage at 15' - a new system.

As I was navigating through NFPA 13 2022 Chapter 21, I came to 21.4, which seems to be where I should be.

My question is: 21.4.1.1.1 is where you start, which states that if it's a new sprinkler system, the demand shall be determined in accordance with 24.4.1.2.2.1. BUT, I skipped that and went on to 21.4.1.2.1.1, which seems to be for the EXACT SAME CRITERIA (unless I cannot read/comprehend, which is possible)!

So when would you use 24.4.1.2.2.1 over 21.4.1.2.1.1?

When we use 24.4.1.2.2.1 with the modification chart, we get a density of 0.297, and when we use 24.4.1.2.1.1, it calls for 0.30.

So they're pretty much the same... but I'm not seeing why you would ever use 24.4.1.2.1.1 since 24.4.1.1.1 directs you to 24.4.1.2.2.1 and bypasses the other. Hopefully, this makes sense.

---
​
21.4.1.1 General

  21.4.1.1.1 Ceiling sprinkler water demand for new systems shall be determined in accordance with 21.4.1.2.2.1 for single and double row racks or...

  21.4.1.1.2 Ceiling sprinkler water demand for the modification of existing systems...

21.4.1.2 Protection Criteria for Single or Double-Row Rack Storage of Class I-IV Commodities over 12 ft Up to and Including 25 ft in Height.

   21.4.1.2.1 New Systems Criteria for Single- or Double-Row Rack Storage of Class I-IV Commodities Stored Over 12 ft Up to and Including 25 ft in Height.

      21.4.1.2.1.1 For single- or double-row racks for Class I, II, III, or IV commodities, encapsulated or nonencapsulated, the ceiling sprinkler demand.... shall be selected from the criteria in Table 21.4.1.2.1.1(a) through Table 21.4.1.2.1.1(c) that are appropriate for... and shall be modified as appropriate by 21.4.1.4.

---

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Pete H
4/10/2026 06:24:16 am

I think it's just a redundancy. It's changed in 2025 edition to 21.4.1.1 being general and only referring you to use 21.4.1.2 for single row and double row, 21.4.1.3 and 21.4.1.5 for multiple row.

Reply
Dan Wilder
4/10/2026 09:45:06 am

I think I am missing something....The sections referenced above from Chapter 21 have no reference to 24...

"So when would you use 24.4.1.2.2.1 over 21.4.1.2.1.1?"

24.4 is "Hose Stream Allowance and Water Supply Duration"?

Assuming you meant to stay within Chapter 21:

Otherwise, this is a single point design density (Section 21.4.1.2.1) change as all the referenced curves we have been using are now existing systems (21.4.1.2.2) now fall into the revised name of:

21.4.1.2.2 Evaluation or Modification of Existing Systems for Single- or Double-Row Rack Storage of Class I Through Class IV Commodities Stored Over 12 ft (3.7 m) Up to and Including 25 ft (7.6 m) in Height.

Reply
Jose R Figueroa
4/10/2026 01:09:18 pm

Right from the NFPA for a new overhead sprinkler system, such as your in-rack Class IV at 15 ft storage height, do not use the modification chart or figures — instead, rely on the New Systems Criteria tables.

This is the exact distinction that NFPA 13 (2022) makes in Chapter 21.4.1.1, which explains why the two sections look similar but are deliberately separated.

Quick Overview of the Sections (NFPA 13 2022)

- 21.4.1.1.1 (the initial paragraph) — Ceiling sprinkler water demand for new systems must be determined according to the New Systems Criteria (21.4.1.2.1 and its tables).
(Note: In your original post, there was a typo — it’s 21.4, not 24.4. Everything stays within Chapter 21.)
- 21.4.1.1.2 — This paragraph applies exclusively when evaluating or modifying an existing system, which refers to the Evaluation/Modification Criteria (21.4.1.2.2 and its legacy curves/figures, plus the modification chart).
- 21.4.1.2.1 — “New Systems Criteria...' 21.4.1.2.1.1 instructs selecting the density per area from Tables 21.4.1.2.1.1(a)–(c) (the new tabulated values).
For your specific case (Class IV, 15 ft storage, single- or double-row rack, CMDA overhead), the table shows 0.30 gpm/ft², generally over a 2000 ft² design area. No interpolation or modification chart is needed.
- 21.4.1.2.2 — “Evaluation/Modification of Existing Systems Criteria...” This section (and 21.4.1.2.2.1) allows using legacy density curves/figures from the 2019 edition, along with the modification chart in 21.4.1.4. The 0.297 gpm/ft² value results from interpolation on the old curve plus an adjustment using the chart. This path is explicitly prohibited for new systems.

Reason for the Two Values (0.30 vs. 0.297)

The 2022 edition intentionally “froze” the new-system tables at standardized, clear densities—often based on a 2000 ft² design area—to ensure consistency and simplify design for new installations. The legacy curves and modification chart were kept only for existing systems, so owners aren’t required to replace sprinklers due to minor code updates. That’s why the modification path might give a slightly different, sometimes lower, number.

Bottom Line for Your Job
- For a new system, only use Tables 21.4.1.2.1.1, which provide 0.30 gpm/ft².
- Never apply the modification chart (21.4.1.2.2.1) for a new system.
- The standard explicitly directs you away from it in 21.4.1.1.1.

If the AHJ asks why you didn’t use the modification chart, just cite 21.4.1.1.1 and 21.4.1.1.2 — the code clearly separates these requirements.

(There was also a minor erratum (13-22-3) that restored the 2019 figures for existing systems, but it does not affect the new-system table values at all.)

You’re all set with 0.30.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT