I have a project using ESFR under NFPA 13-2022 Edition.
Section 14.2.11.3.4 states that an obstruction will not be combined if the distance to the adjacent obstacle is greater than three times the width of the adjacent obstruction. The appendix states the minimum distance to another obstacle as three times the diameter of the pipe. For example, I am analyzing a 1 foot wide vent duct and a 2-inch pipe. Should they be 3 feet apart, or 6 inches apart, in order to consider each item it's own obstruction? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
9/11/2024 09:47:10 am
What is the position below and to the side of the sprinkler?
Reply
Jack G
9/11/2024 10:03:35 am
I go to the fm guidelines for ESFR s. They have led the way on this. They have nice pictorial scenario s the describe and you can visualize the results.
Reply
Casey Milhorn
9/12/2024 11:11:04 am
See link below:
Reply