NFPA 13R, Section 6.6.5.1 (2019 Edition) requires sprinklers to be installed to protect balconies, decks, etc, that serve dwelling units.
What constitutes the definition of "serving dwelling units?" If we have a landing over a stair in an exterior corridor, would that landing over the stair "serve a dwelling unit?" This is a situation that the inspector is now bringing up at the end of the project and is requiring protection, even though the plans were approved, stating that this area was not to be protected per sections 6.6.5 and 6.6.5.1. Please see the attached picture and let me know your thoughts. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Brett
4/20/2026 07:13:52 am
In my opinion 6.6.5.1 does not apply here. That section is in 13R because of IBC (2021) section 903.3.1.2.1 which says "balconies, decks, and ground floor patios of dwelling units and sleeping units". It doesn't say anything about "serving" dwelling units.
Reply
Todd E Wyatt
4/20/2026 08:28:45 am
I agree with Brett ... start with the scoping Code (e.g. IBC-2024) to determine WHERE an automatic sprinkler system (ASPS) is required (see IBC 903.2 Where Required in REFERENCES below), then determine WHICH ASPS system is permitted (see 903.3.1.2 NFPA 13R Sprinkler Systems), and then determine HOW the ASAP is to be designed, installed, and inspected per the referenced Standards (e.g. NFPA 13R - 2022 per IBC-2024).
Reply
Todd E Wyatt
4/20/2026 08:29:36 am
REFERENCES
F Marvitz
4/20/2026 09:58:29 am
My comment is to remind designers, and contractors that just because a set of plans is approved, does not mean the design is free from missed items or code compliance.
Reply
Todd E Wyatt
4/21/2026 08:43:07 am
Agreed!
Reply
Mark Harris
4/21/2026 09:30:59 am
Agree with comments that need to look at this if it is an egress that needs protection. My understanding is history of requiring sprinklers on decks, patios accessed from dwelling unit was from hazard people created from what they stored or did on the patio or deck.
Reply