When dealing with combustible soffits, what are the conditions where a soffit is big enough to warrant a sprinkler inside?
In our case, we have wood constructed soffits with sprinkler protection below and adjacent to the soffit. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/13/2025 07:40:15 am
This is talking about exterior soffits:
Reply
Glenn Berger
3/13/2025 08:10:56 am
Need more information to provide guidance.
Reply
Ricardo Gonzales Jr
3/13/2025 08:31:22 am
An added question is: Is the interior of the soffit accessible? Like some hard ceiling rooms with 5' of space between the ceiling and deck, the space is not accessible therefore not required to be sprinklered. If you can't access it, why install it?
Reply
Wes
3/13/2025 08:37:21 am
That’s not necessarily true. If this is an NFPA 13 system and the concealed space is combustible, then it would require sprinkler protection (unless it meets one of the listed exception scenarios).
Reply
Jesse
3/13/2025 08:34:08 am
To add to Ricardo and Glenn's questions, is this a full NFPA 13 system or 13R / 13D?
Reply
Dave L.
3/13/2025 11:03:03 am
I assume this is an NFPA 13 application, and in the 2025 edition, 9.2.1.11 offers a way out: "Concealed spaces created by soffits of combustible construction below noncombustible or limited combustible ceilings separated into volumes each not exceeding 160 ft3 (4.5 m3) by noncombustible or limited combustible materials shall not require sprinkler protection."
Reply
Jack G
3/13/2025 05:47:29 pm
I think what Ricardo was meaning is that if there are concealed combustibles in a blind space ( with no access ) and fits the NFPA 13 definitions then sprinklers would not be required but the space below it the minimum design area must be increased to 3000 ft2.
Reply