What Safety Factor to Use for Fire Flow?

1/7/2026

12 Comments

 
In the absence of a code-mandated requirement, what safety factor ​should we apply when evaluating fire flow, if you apply one at all?

I am currently working on a building that has a code-required fire flow of 2,000 gpm at 20 psi. Using the MeyerFire Toolkit to evaluate the water supply, I found
that the available fire flow is 2,004 gpm at 20 psi.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
12 Comments
Dan Wilder
1/7/2026 07:28:40 am

I may be off on this, but I have never heard of a safety factor requirement (mandated or self-imposed) as it relates to Fire Flow vs water supply. You just need to achieve that minimum flow at 20 PSI.

Now, hydraulic calculations utilizing that same water supply does need to meet safety factors, but those are separate and independent of each other.

Reply
Anthony
1/7/2026 08:05:36 am

Is a safety factor required, no. But I'd be more worried about an additional flow test that charts out lower then your 2000@20. If you have a slow project and the FP designer needs a new test within 12 months of design and you don't have that then you'll have to figure it out. If you're in the planning stages now I would preceded as if you don't need to update the water flow and leave a contingency budget item and document the risk with your client - assuming you're on the consulting side.

Reply
Franck
1/7/2026 08:14:26 am

Normally, no safety margin requested.
In your case, you’re fine.
But in your case you also have no safety margin for possible fluctuations, during the day or during the year (at some locations, water supply may fluctuate due to changes on demand, because of seasonal activities, or fluctuating process water needs).

Reply
Glenn Berger
1/7/2026 08:26:20 am

As others have said no safety factor is required. However I would ask for additional hydrant flow test to be conducted at various times of the time and then come back to check seasonal variances (ss Franck indicated). Be on watch for aging of the existing system which will lower the available conditions.

P.S. The red line in your graph plotted incorrectly. You have a dot at 1500 gpm / 20 psi.

Reply
Craig Prahl
1/7/2026 08:37:41 am

One big thing I'd recommend is to verify that the 2000 gpm flow rate is actually attainable and available from the water supply. You can calculate anything but reality versus theoretical may vary. To your original question, there is no need to apply any kind of safety factor. There is no code or other requirement to do so. Also, for fire flow, there is a duration, be sure the water supply has adequate volume to provide for the required duration and that the local water purveyor is agreeable to that amount being depleted. In some jurisdictions water consumption is limited and large volume fire flows are expected to be provided via an owner provided water tank.

Reply
Jesse
1/7/2026 08:57:58 am

I'm generally not concerned about a safety factor for fire-flow. We want to ensure that the residual pressure is >20-psi, or higher if required by the AHJ

Reply
Mark Harris
1/7/2026 08:58:16 am

All great comments. Note Dan's comment that the sprinkler system calculations will need a safety margin (Reduce curve by 20% of static pressure in my area but that is up to your AHJ). So that supply may be fine for code fire flow it still could require a pump and possibly water tank some sprinkler systems. Depends on hazard and height of building. 60 PSI not much to start with.

If fire flow is the only concern at this stage that curve is close enough that I suggest a discussion with the water supplier and AHJ to determine if test is acceptable and if fluctuations could be a factor.

Reply
Jay
1/7/2026 09:08:05 am

Appears you have a system demand of 1500gpm with a 500gpm outside hose allowance.
I recommend performing another water supply test and flowing at least 2000gpm to see what's actually available. You flowed only 1000gpm on the water supply test being used and have extrapolated the results to 2000gpm, which is only a guestimate.
The water supply test results are required to be modified to account for daily/seasonal fluctuations and future demand on the water supply system (aka safety factor), however there is no prescriptive safety factor.

Reply
James Art, FPE
2/4/2026 02:58:08 pm

Good Point!

Reply
Jack G
1/7/2026 09:19:58 am

I m a believer in supply calcs. Because it’s “ real” based on the flows and pressures at the time of system ( entire MRA) activating .
If a system is “ demand calculated to 10% say) if you were to perform a supply calc right after—- your system will not deliver ( due to increased pressure, friction losses) the system demand.
Pipe sizes must be balanced to allow the system demand at the lower pressure, and not allow increased flow which will increase the pressure( additional loss thru the pipe creating deficiency)
So I do both. ( Easy on the hydraulic programs)
( balance pipe sizes ) then do a demand calc with a safety factor.

Reply
David Kendrick
1/7/2026 10:15:43 am

Before any data is published it has been tested as sufficient and included with that is a built in safety factor.

Reply
Brett
1/7/2026 11:02:11 am

Others have already answered your question. If you don't mind some unsolicited advice I recommend getting another flow test done. That is a pretty steep drop off. See if they can do a two outlet test or open up another hydrant to get a higher flow from the test so you're not depending on such a big extrapolation.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT