MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

What is the Existing System's Design Criteria?

8/7/2025

6 Comments

 
This is a backflow preventer retrofit project where I'm trying to figure out what the system's original design criteria was.

I am working with an existing 7,300 sf warehouse area within a larger building, which includes offices and a workshop. It is a marine operation, and the products stored are primarily spare boat parts, propellers, shafts, brackets, housings... large metal objects stored in wood crates or cardboard boxes.

I have determined this to be Class II Commodities, stored no higher than 20'.

I am thinking that, based on NFPA 13-2019, Table 21.4.1.2 and Figure 21.4.1.2(b) curve B, I need a density of 0.3725 gpm/sf over a 2,000 sf area. I would also be required to have a maximum protection area of 100 sf based on Table 10.2.4.2.1(d).

Here's where it gets tricky - the branches are spaced roughly 15' apart, and heads are spaced 8' or more along the branch line. Some are as far apart as 11'-6". The heads are K8.0 solder-type. Because of the K-rating, this shouldn't be a pipe schedule system.

Is anyone aware of an alternative storage protection method that this system may be designed to?

The installation date is 1986. ​Any thoughts would be greatly appreciated. I do not know what density I should be applying to this area in my calculations. Thank you very much!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
8/7/2025 06:42:57 am

Without the original installation plans and what you have said, there is no way to be certain:

The earliest "Free Access" NFPA gives me on NFPA 13 is 1991 edition, so I'm already off by at least five years on this comparison... but in Table 4-2.2 "High Piled Storage" is just noted to have a maximum of 100 square feet. I'm not yet seeing the current restriction of no spacing exceeding 12'-0" between heads (except between bays of 25'-0" where it can go up to 12-6)

Wait, Section 4-4.1.1 does have the maximum distance for sprinkler spacing in high-piled storage as 12'-0".

-

Okay, so at least by 1991 you couldn't have 15-0 between branch lines in high piled storage.

-

Honestly, I have a feeling this was designed as "miscellaneous storage" and OH2 and just poorly enforced for decades. It's unfortunately more common than you think.

Reply
Anthony
8/7/2025 07:16:13 am

Without a set of plans or hydraulic placards its very hard to determine the "original design criteria." In these cases engaging an AHJ and showing a flow test and the backflow loss pressures can be a good place to start. This can be effective if there is a ~3psi drop at a reasonable flow rate that's a rounding error in most hydraulic measuring methods.

Reply
Jesse
8/7/2025 08:13:07 am

The spacing makes me lean to this having been a different occupancy at one point and then someone coming in and making it storage without assessing the capability of the AS system. If I had a dollar for everytime I've seen that, I'd have a bunch of dollars.

I would highly recommend a design survey and then reverse engineer the system to ascertain the actual density provided.

Reply
Glenn Berger
8/7/2025 08:46:19 am

The installation date was 1986, so the design date was possibly a few years earlier. Sprinkler system coming up on 40 years in service.

You are in the timeframe when storage was covered by the NFPA 231 series of standards. When criteria was a lot more basic than it is today.

I am with Jesse on this one and wish you luck.

Reply
Jerry Clark
8/7/2025 10:55:58 am

Your storage qualifies as Class II Commodities—primarily metal parts packaged in wood or cardboard, with noncombustible or limited-combustibility packaging. According to NFPA 13-2019, Table 21.4.1.2, the required CMDA (Control Mode Density/Area) design density for such commodities stored up to 20 feet is 0.3725 gpm/sf over a 2,000 sf area. Additionally, Table 10.2.4.2.1(d) limits the maximum coverage area per sprinkler to 100 sf.

However, your sprinkler arrangement presents challenges. The heads are spaced 8 to 11.5 feet apart along branches that are 15 feet apart, which means some sprinklers protect more than 100 square feet—exceeding the maximum allowed for hydraulically calculated storage systems at the necessary density.

The existing K8.0 solder-type heads are standard spray sprinklers, not storage-specific (CMSA or ESFR) models, which were not available in 1986. As a result, the original system likely does not comply with current storage protection standards.

Because the system was installed in 1986, it followed an earlier edition of NFPA 13, which required lower densities for storage. Current editions of NFPA 13 allow some flexibility for existing systems—particularly under Chapter 26—but do not grant blanket exemptions. Significant changes in commodity class, storage height, or use generally still require system upgrades.

One approach is to evaluate the system under the provisions for modifications to existing systems. The current code allows “evaluation/modification” for previously installed systems, but sprinkler coverage and density must at minimum meet the requirements in effect at time of original installation. Density cannot be decreased below the intent for that commodity class and arrangement.

It is also possible that your system was installed as a pipe schedule design even with K8.0 heads, since the 1980 edition of NFPA 13 and later only permitted new pipe schedule systems for light and ordinary hazard occupancies. However, local codes in effect at the time of construction may have referenced an older edition, so you should try to verify the applicable standard for your jurisdiction.

The best next step is to consult with your AHJ. If a full NFPA 13 retrofit is not practical, discuss possible alternative risk mitigation strategies (such as additional fire detection, limiting storage height, widening aisles, or enhanced manual fire response plans). Ultimately, acceptance of any alternative is up to the AHJ, and decisions should be formally documented.

Reply
Jack G
8/7/2025 10:51:36 pm

Class 2 commodities in the 80 s was under NFPA 231, 231 c ( for racks vs palletized) .
I m assuming storage on pallets.
There were 2 curve charts, on for 20 ft high storage, standard temp heads and another for high temperature heads.
The second chart allowed for a 25% reduction in area but not less than 2000 sq ft.
There was a percentage chart for less than 20 ft storage.,
Looking at my archive copy the density would be about a .17 over 2000 sq ft .( not .3725) Which was very common density. I d try to sell the customer on 100 sq ft spacing ( more sprinklers ) for greater tenant flexibility.
I can’t count how may 130 s I ve changed to 100 sq ft 10 years later for a new tenant.
Densities less than .25 allowed 130 sq ft and 15 ft max spacing.
Greater than .25 was 100 sq ft. 12 ft spacing except for 25 ft bays.
I m not sure why the new rules / density would be so high for class 2 but I ll look into it. My off the top of my head guess is ( new) it should be around a .23. But I ll look.
Regardless the system is grandfathered unless the storage has changed.
A trip to the building department and reviewing the CO docs will tell you exactly.,

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT