What is the Design Area for 600 sqft Dry System?

9/13/2024

9 Comments

 
I'm designing a dry system feeding an area of about 600 sqft. It's a Light Hazard area, so the design criteria is just 0.10 gpm/sqft over 1,500 sqft.

Should the design area include the entire area, or could I just calculate the 5 most demanding sprinklers?

Per NFPA 13 2016
, Section 11.2.3.2.3.2 under the quick response sprinkler section states, "The number of sprinklers in the design area shall never be less than five."

The section above that does state that the area of operation can be reduced
, but that only applies to a wet pipe system, amongst a few other points. Of course, this is a dry system, so I don't believe the reduction can be used for this situation.

How should this design area be calculated?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
9/13/2024 06:50:49 am

I'd do the whole area of the system unless it's just a 600 square foot corridor being fed, then I'd just do the five pursuant to 11.2.3.3.6 (and if you're using extended coverage, all sprinklers within 75 linear feet of corridor's worth).

But take it with a grain of salt, there might be exception you can use that I'm missing.

Reply
Pete H
9/13/2024 08:15:04 am

I also forgot, you need to add a phantom flow if you're not hitting the minimum flow for the required square footage and density if you're doing the Density/Area calc and not room design.

Reply
Mike Morey
9/13/2024 08:10:13 am

If you have less than the required area you calculate the entire area. That said, you may be subject to "phantom flow" (see 23.4.4.2.4 and 5) in that case. If you meet the requirements to call it "room design" however, phantom flow doesn't apply, so that is probably going to be the preferable route to go.

Reply
JI
9/13/2024 08:10:46 am

I would add a "phantom flow" as per 23.4.4.1.1.5 NFPA 13 2013 to the design area if it is a room within a building that has other sprinkler systems around it. I would most likely add this flow to a base of riser or connection to the wet piping for the dry pipe.

Of course there are other design methods that may apply such as the corridor calculation mentioned above by Pete that may be considered.

Reply
Glenn Berger
9/13/2024 08:14:10 am

Need more information before advising on an answer -

What is surrounding the new dry-pipe sprinkler system area? Are there other hazards protected by separate sprinkler systems? Is the 600 square feet bounded by fire-rated construction?

Reply
Matthew Ostroff
9/13/2024 08:14:54 am

I believe you need to have a minimum of 195 gpm (.1gpm/sf x 1,950 sf) calculated for a dry system to meet the requirements of 27.2.4.2.4 of NFPA 13 (2019). You would need to add back in the flow at the furthest cross main.

27.2.4.2 Density/Area Method.

27.2.4.2.1*
Where the design is based on the density/area method, the design area shall be a rectangular area having a dimension parallel to the branch lines at least 1.2 times the square root of the area of sprinkler operation (A) used, which shall permit the inclusion of sprinklers on both sides of the cross main.

27.2.4.2.2
Any fractional sprinkler shall be carried to the next higher whole sprinkler.

27.2.4.2.3
In systems having branch lines with an insufficient number of sprinklers to fulfill the 1.2 requirement, the design area shall be extended to include sprinklers on adjacent branch lines supplied by the same cross main.

27.2.4.2.4*
Where the available floor area for a specific area/density design criteria, including any extension of area as required by 19.2.2 and Section 20.10, is less than the required minimum design area, the design area shall be permitted to only include those sprinklers within the available design area.

A.27.2.4.2.4
The following steps outline the procedure for calculation in accordance with 27.2.4.2.4:

(1) Calculate the hydraulic design discharge including those sprinklers within the available floor area.
(2) Calculate the minimum required discharge by multiplying the required design density times the required minimum design area.
(3) Subtract the discharge calculated in Step 1 from the discharge calculate in Step 2.
(4) Where the discharge calculated in Step 3 is greater than 0, the hydraulic design discharge is recalculated including an additional flow equal to that calculated in Step 3. The additional flow is added at the point of connection of the branch line to the cross main furthest from the source.
(5) Where the discharge calculated in Step 3 is less than or equal to 0, the hydraulic design discharge is as calculated in Step 1.

27.2.4.2.5
Where the total design discharge from these operating sprinklers is less than the minimum required discharge determined by multiplying the required design density times the required minimum design area, an additional flow shall be added at the point of connection of the branch line to the cross main furthest from the source to increase the overall demand, not including hose stream allowance, to the minimum required discharge.

Reply
Anthony P
9/13/2024 08:22:41 am

Keep in mind Dry Systems are required to be designed to 1950 Sq Ft.

New York is a little Different but usually I would design it to the actual size of the Dry System because if you have an Air Compressor you need to know the Volume of the Dry System (Inspectors test needs to be located at the most remote Branch)
Worst Case if there is an adjacent Wet System run a Separate Calculation on that. (Extra Price of course) Cause how I look at it either the Dry system is going to go off or the Wet System.

Usually, I would bounce this off the AHJ. Since they will sign off on it.

Reply
Jack G
9/13/2024 09:16:42 am

Calculate 1950 sq ft. Add sprinklers from adjacent areas if dry.
If adjacent areas are wet add a phantom flow at nearest x main..

Reply
Jesse
9/13/2024 10:05:40 am

Well, it wouldn't be 1500 sq. ft to begin with. Adding the 30% it becomes 0.10 / 1950.

But since its only a 600 sq. ft area protected you'd calc the whole thing. And you might need to add phantom flow to get to you minimal flow requirements

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT