What is Best Practice for Testing Forward-Flow?

10/7/2024

9 Comments

 
Regarding forward-flow testing, I have read that a main drain (if sized appropriately) can be used in place of other means. This was in the 2016 NFPA 13 A.8.16.2.4.2, but I cannot locate it in the 2019 version.

With that, what is the best practice for testing at the time of system acceptance?

Without being able to use a hose monster, is the main drain test sufficient to ensure the backflow fully opens?

Other than hydraulic calculations, how is it proven that we have an acceptable result?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
10/7/2024 08:11:13 am

If you can achieve system flow (with or without hose allowance as applicable) through a main drain (using a smooth bore orifice or other means to get a decently non-turbulent pitot reading) then yes, it is acceptable (Say a 2" drain on a light hazard system which is very possible)

Adding a mech tee and hose valves on the riser is another option, generally 250 GPM per hose valve up to the system demand.

Using NFPA 25-23' 13.7.2.3 is the next option but as this would likely go back to 13-1996 when forward flow testing was first added, may not be acceptable for acceptance testing only ITM after the fact.

"Where connections do not permit verification of the forward flow test at the minimum flow rate of system demand, tests shall be conducted at the maximum flow rate possible."

Meyer Fire Main Drain Estimation Tool
https://www.meyerfire.com/blog/a-new-balanced-main-drain-estimator-tool

Reply
Chad
10/7/2024 08:26:22 am

Most guys put in a Tee off the riser with a normally closed valve feeding into the FDC when there is not a standpipe. We allow this for most simple systems.

Reply
Tom Jordan
10/7/2024 08:32:31 am

We've been installing dedicated test headers in new campus buildings. In existing buildings, we're either installing a header or installing a bypass (with a supervised normally-closed control valve) around the FDC check valve. During forward flow testing, the valve is opened and the FDC is used as the point of discharge.

Where we have fire pumps in place, the annul flow test also satisfies the forward flow requirement.

Reply
Matthew
10/11/2024 08:29:37 am

Tom, I'm interested to hear your experience with the bypass method. Have you used it with a siamese connection? I could see it working with a storz but figured it wouldn't work with a siamese due to the internal clapper.

Reply
Anthony
10/7/2024 08:50:50 am

With that, what is the best practice for testing at the time of system acceptance? Using a hose monster. But really you should be able to see with a flow switch test if there is any problem with the backflow upon install. this is not the point of backflow testing. The point is making sure nothing is obstructing the paddles.

Without being able to use a hose monster, is the main drain test sufficient to ensure the backflow fully opens? yes as long as the main drain can handle sufficient flow. you have a K factor on you test and drain so you can figure out how much water is flowing given a pressure.

Other than hydraulic calculations, how is it proven that we have an acceptable result? I'm not sure what your asking? you need to have as much water come out of the test port as is required by the hydraulic placard information.

Reply
Jack G
10/7/2024 10:43:43 am

Agree with above comments.
Couple of things I do are:
After the. Bfp I add a tee and butterfly valve ( size of underground lead in ) and a piece thru the wall with a gr cap. ( new installation permanent test rig) . To test bfp forward flow — I bring a test header with valves, and test.
On new installs I first flus the underground. Then install the bfp. And test header. Test. Then finish the valve room leaving the permanent rig above

Reply
Mark Harris
10/8/2024 11:58:43 am

On flushing through the FDC what about the internal clappers acting as check valve to prevent flow out?

Reply
Jesse
10/9/2024 08:13:11 am

I'm a little late to the party, but better late than never.

The main drain is probably not sized adequately. However, the FDC might be. We've had technicians turn the FDC check valve around and forward flow test that way.

Ideally, a firward flow test header outside is ideal. But if the GC doesn't want that, I'll add 2.5" hose outlets on the riser above the flow switch.

Reply
Andre Bourgoin
10/17/2024 08:13:04 am

Adding a forward flow test connection on existing system, I would try to use the bypass to the FDC with a N/C valve (remove clapper in the check valve), or add a valve somewhere on the system. On a new system install a dedicated test connection, in the presence of a fire pump then install a combined pump/backflow test connection.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT