What Happened to Hydrants in Pacific Palisades?

1/20/2025

5 Comments

 
Keeping politics out of it, what most likely happened to the fire hydrants in Pacific Palisades, California?

Or looking at both possibilities, what likely happened if all water reservoirs were full and what likely happened if the reservoirs were empty or under repair?

I presume 40 or 50 fire pumper trucks over-taxed a perfectly functioning water system to the point where supply tanks could not be replenished fast enough.

Additionally is a California water reservoir a body of treated water that fills the underground piping system & storage tanks? Or, is a reservoir a body of water (near by) that is waiting to be treated, and then enter the distribution piping?

Looking for a better understanding from those that might be more informed and knowledgeable on the subject here. Thanks.

Moderator's note: Major cultural events have a tendency for discourse to go political quickly. This is a technical forum for technical discussion on topics relevant to the fire protection industry, and not a location for political discourse. We welcome and appreciate civil discourse that's informative and helpful. Please refrain from political commentary as it will be removed from this site. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Manny
1/20/2025 08:12:36 am

I am of the opinion that the systems were over taxed with everyone connecting to them at once. Only so much water to go around, either going to have little or no pressure or no water at the hydrants. The supply could not keep up with the demand.

Reply
Jackson
1/20/2025 08:28:18 am

Or looking at all possibilities, what would happen if all water reservoirs were full and what would happen if all the reservoirs were empty or under repair? Common sense would tell anyone that has the ability to use it you don't enter into something that happens yearly unprepared. Being born and raised in CA, this happens every year, just not to this magnitude. Areas that have large snow amounts prepare before the storms start. But common sense and politics are like oil and water, they don't mix. And common sense or the ability to use it seems to be in short supply these days.

Reply
Dan Wilder
1/20/2025 10:10:24 am

Armchair, Monday morning assumptions here....points are in no particular order.

-The fire started on the upper elevations of the water system in more wildland areas where the services were spread out for water draw and attack options.

-As the fire moved into more residential areas, the water demand increased as additional crews were put into offensive/defensive positions.

-As crews pulled back into lower elevations at varying times or additional crews responded setting up new attack points (think a saw tooth pattern), the water demand was further stressed at lower elevations removing additional needed pressure at the upper elevation locations.

-Home owners start makeshift protection efforts (minimal but still a demand) and leave the area, couple this with structures that are engulfed and collapse damaging above ground water lines creating an uncontrolled water discharge situation.

-I'm assuming the water supply started high and went downhill so any pressure boost they may have received would have been reduced from all the higher elevation structures that were lost and freely spilling water. If there were pump stations involved, power would have been an issue assuming the equipment was operational through all the heat.

-Standard pumper truck puts would 500-1500 GPM so let's average it to 1000 GPM x 10 trucks (not a tough number to get to with the responding departments sending crews and well below your 40-50 originally posed) means an average draw of per hour of ~600,000 gallons. That's a duration of 5 hours for the 3x 1-million-gallon water tanks that were available, maybe stretch that for water refill so lets say 8 hours...that fire was reported at 11AM and burned for several days so a losing battle of attrition. The article linked below showed that they depleted all three tanks within the first 16 hours of the fire.

-I do not think there is a method of just opening up a potable water system to non-potable water source so even with the reservoirs full, what is the capacity of the system to treat the water to be reintroduced back into the water supply?

There are a lot of other factors like the ability of the water supply to even handle a fire progression like this, urban firefighters working wildland fires, access to the fire in the early stages, the drought, hardening efforts of the structures, no air support, fast progression of the fire due to weather, and even more operational items like budgets and infrastructure. This was more a domino progression of bad things that individually were items of concern but cumulatively are disastrous.

https://laist.com/news/climate-environment/why-did-pacific-palisades-water-hydrants-run-dry

https://en.wikipedia.org/wiki/Timeline_of_the_2025_Palisades_Fire

Reply
Shawn
1/22/2025 10:30:02 am

I think it was the perfect storm. All of the above caused the massive failure.

Reply
James E Art Fire Protection Engineer (FPE)
2/1/2025 06:49:07 pm

Here's an article about this:
https://www.eastbaytimes.com/2025/01/24/trumps-claims-about-california-water-and-l-a-fires-are-inaccurate-and-misleading-experts-say/

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT