My management wants hydrant flow tests to achieve a minimum 10% pressure drop, even if that means opening additional hydrants. However, some municipalities are very reluctant to flow additional hydrants because of the amount of water being wasted.
I understand the importance of obtaining accurate water-flow information, but this raises a few questions. If the city provides a flow test with less than a 10% pressure drop, is it really necessary to open additional hydrants just to meet that recommendation? Since NFPA 291 is a recommended practice, is the 10% pressure drop an absolute requirement, or can the available water-flow information still be used if it adequately supports the sprinkler system's hydraulic demand? And here is the question I find most interesting: How many fire sprinkler projects have we all estimated, designed, submitted, and successfully installed over the years using water-flow information that did not achieve a 10% pressure drop? I am not questioning the need for accurate testing. I am questioning whether requiring additional hydrants to be opened in every situation is necessary, especially when municipalities are concerned about water conservation. I would be interested in hearing how other estimators, designers, engineers, and AHJs approach this issue. How many times do I have a water flow without a 10% drop, a lot! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
10/27/2026 06:10:08 am
I feel like this can be accomplished just by incorporating the historical lows or raising the required safety factor for plans rather than these tests which, as pointed out, waste water.
Reply
Dan Wilder
10/27/2026 07:42:54 am
291 is a recommend practice so as you said, that entire document is a "should". Now, if the local AHJ has adopted language that is more restrictive, you would be required to follow that. There is always the "artificial" 10% restriction, not to be confused with the system safety factor, that can be applied to the results of the test.
Reply
Anthony
10/27/2026 07:44:15 am
10% is a good idea - just that not a technical necessity. I'd be more interested in how close you get to your system design point.
Reply
Jesse
10/27/2026 08:16:18 am
NFPA 291 is a "recommended" practice. The 10% drop is only part of it. The other part is obtaining the required flow.
Reply
Glenn Berger
10/27/2026 08:22:44 am
You will need to describe the existing water infrastructure to explain why the recommended pressure drop cannot be achieved.
Reply
Jack G
10/27/2026 09:54:10 am
A lot of water companies will flow a 4.5 inch on the hydrant for a sprinkler water flow test. Or 2 , 2.5 inch if there is not a 4.5 inch. If you achieved your flow and it doesn’t meet 10% pressure drop you have also satisfied 291.
Reply
Streeter
10/27/2026 10:37:55 am
Recommendations are not requirements, but are suggestions for best practices.
Reply
RyanO
10/27/2026 02:41:46 pm
As several have noted above, as long as the hydrant flow exceeds the demand of the sprinkler system I'm good with the test. I tell our team to flow enough outlets to get a point on the curve somewhere beyond the demand. Percentage of pressure drop is less concerning.
Reply