MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Water Storage Tanks Similar to Fuel Storage?

8/7/2026

3 Comments

 
I have been introduced to a project that involves six underground water storage tanks and an external pump house that will provide fire protection water to a fully sprinklered building.

​We have been informed that the sprinkler contractor will be providing the building sprinkler system design, but not the underground storage tank portion of the project.

The firm I work for performs a significant amount of fueling and convenience store design work for gas station and convenience store clients, but I am curious whether these water storage tank options are similar in nature to underground fuel storage tanks and their associated pumping equipment?

Obviously, the medium is different (water versus fuel), but I am interested in understanding whether there are comparable design considerations, equipment types, or industry standards.

Any guidance, resources, or lessons learned would be greatly appreciated. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Mark Harris
8/7/2026 10:42:52 am

Here is good place to start: https://xerxes.com/fire-protection-water-tanks/

Assuming the pump house will be above grade the pump will need to be vertical.

Reply
Jack G
8/7/2026 10:44:00 am

First of all you must choose the type of underground tanks fiberglass and or steel.
The tank must be listed per NFPA 22.
Pressure test the tanks for leaks or cracks. 5 psi for 24 hours. ( while on the truck);
If fiberglass, and is used for a combination domestic/ fire water it must be an internally coated set of tanks. ( for domestic water);
The tanks must be set and secured , on its own foundations with saddles and pea gravel is used to fill in. This is to prevent buoyancy as the tanks empty, and use a buoyancy calculator. Pea gravel is filled in gradually as you fill the tanks with water.
The tanks must be manifolded together using flexible connectors for settlement. Each supply to the manifold must have an anti vortex plate. In the center run your underground combined piping to a cistern of at least 4 ft diameter. ( concrete pipes like drainage with joint gaskets and patched over with fiberglass. The cistern must have a sump 2 ft deeper than the bottom of the underground pipe.
The size of the tanks, manifold pipe and fire pump supply to the cistern must be sized for the hazard and minimal friction loss. And / or domestic water use if combo tanks.
The tanks shall have proper vents and maintenance hatches and covered with earth to prevent freezing. Diameter of tanks is important.
A factory built pump house with foundations can be used. A vertical pump with shaft and impellers , diesel engine should be used. A submersible jockey pump , electric should also be used.
From the pump house supply your building and or hydrants keeping in mind flexible connectors should be used on piping between foundations.
If combo tanks , an electric domestic pump is used with a BFP.
The domestic water pump must be wired to shut off when the fire pump activates.
Also a method to refill the tanks automatically must be installed. Usually done via shaft type screw in magnetic switches screwed into the top of the tank.
A separate panel ( I use ) to monitor the tanks should also be used. And placed in the pump house with signals to the fire alarm panel ( low water, high water , leak detection etc. review NFPA 22)
Lastly electric and fire alarm wiring to the tanks, pump house, building, is installed within the underground trench. I keep it 3 feet away and use burial tape on top of both.
I hope this helps. Sort of soup to nuts. My first tank job was 56 years ago. I love to do them and try to pick up stuff with each job.
Good luck.

Reply
anthony
8/11/2026 09:12:52 am

"We have been informed that the sprinkler contractor will be providing the building sprinkler system design, but not the underground storage tank portion of the project."


This is fairly typical for sprinkler contractors, They're typically not underground work experts. Lots of easy ways to lose money if you're not doing this work frequently.

As Jack says above NFPA 22 is the pace to start for detailed specifics.


For generalities to your situation there is less focus on keep fuel out of the ground and more focus on keep the volume of required water in the tank. There will be level gauges but those will probably be connected to an auto fill feature from domestic/city water or a well. You may need to prove a water trucking contract to fill the tanks upon testing or other uses and have a buffer. (depending on the AHJ- yes I've had to do this). You'll need to confirm if there are hydrants that come off this tank (see questions from earlier this week) and determine fire flow. Heating will be a concern compared to gasoline. Venting will be an issue as you suck water out of the tank air needs to get back in this is often over looked by sprinkler folks.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT