How do you size a water storage tank for fire flow when the city supply is significant, but not sufficient for Fire Flow?
For instance, if I have 1,500 gpm available from the city at 20 psi, but I need 2,000 gpm for Fire Flow, is the water storage tank sized for 500gpm for the required duration? Or do I need to size the tank for the entire 2,000 gpm minus reliable refill? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Jose Pinies
5/20/2024 08:09:07 am
Por favor, notificarme por correo los nuevos comentarios de esta publicación
Reply
CJ
5/20/2024 08:29:55 am
Unless local requirements or AHJ say otherwise, you can size for the refill. So in your example, if it’s a 60 minute duration, you need a minimum 30,000 gallon tank (500 gpm x 60 min).
Reply
NK
5/20/2024 08:52:05 am
If the water storage tank is being used to support the fire hydrants I would size the tank for the fire flow.
Reply
Glenn Berger
5/20/2024 09:13:12 am
Need to obtain approvals from the AHJ and other approval authorities before proceeding with this method.
Reply
CJ
5/20/2024 09:37:19 am
After re-reading the question and your response I am a little confused. Would the flow tested 1500gpm at 20 psi not be the ‘reliable’ or ‘proven’ flow rate?
Reply
Dan Wilder
5/20/2024 09:30:00 am
NFPA 22'-23' Ed.
Reply
SK
3/10/2025 02:51:00 am
Why not considered 30,000 as per NFPA 22 section 4.1.6
Reply
Steve Cooper
5/20/2024 09:54:44 am
The tank is sized per fire flow. They want the building to have water even if city supply cuts off. It's a safety factor.
Reply
JH
5/21/2024 08:55:43 am
Reference Chapter 4 of NFPA 1142, 2017 Ed. for your minimum tank size. Run it by the AHJ.
Reply
Jack G
5/21/2024 05:21:19 pm
Your opening paragraph indicates it’s a water “ storage “ tank, for fire flow. ( not a break tank)