Is a library vault filled with Class A banker boxes filled with paper on multiple shelves considered a deep seated fire hazard?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
9/5/2024 08:14:40 am
Paper fires are more likely to be surface-based and not deep-seated type fires.
Reply
Ricardo Gonzales Jr
9/5/2024 08:30:33 am
This sounds like a mental exercise. I agree with Glenn, but also what is needed is data to back up the assumptions for this type of fire. Don't get caught up in the 'What If's and go down the rabbit hole. A fair topic for a master's thesis but not a doctorial one.
Reply
Robert Kessenich
9/5/2024 08:43:05 am
I agree with you Ricardo. I would worry more about the egress from and through the room than I would the boxes and paper. If the boxes are stacked and leaning where they could impede egress by falling...then I make the suggestion of safer storage practice.
Reply
Dan Wilder
9/5/2024 08:42:52 am
I would say borderline yes based on the description of the room and storage. You've got limited access, large fuel load, shielding from solid shelves (assumption here) for lateral fire spread/across isles, possibility of collapse of what is typically a lesser structural frame strength when it comes to this type of shelving or on the flip side, if this is a larger storage rack there are now multiple layers of height & depth for combustible materials.
Reply
Pete H
9/5/2024 10:13:42 am
Don't know how deep-seated it is due to the bankers boxes being cardboard if I'm not mistaken. Like they do get dusty in storage and I could see that making the chance for a deep seated fire similar to sawdust.
Reply
Jack G
9/5/2024 10:15:31 am
I m trying to figure how spontaneous combustion can occur in a closed box within metal frames with doors surrounded by concrete on 5 of the 6 sides.
Reply
Mark Harris
9/5/2024 01:04:59 pm
This question often comes up for clean agent systems and people argue it both ways. NFPA 2001 says no deep seated fires but some opinions are that the detection system actuation and clean agent discharge would be before the fire developed into a deep seated fire (incipient or surface fire stage). If you classify it deep seated for gas system NFPA would be CO2 and extended hold period which has life safety concerns.
Reply
Jesse
9/5/2024 01:54:28 pm
Speaking only for myself and not an NFPA technical committee, I wouldn't consider that a deep seated fire
Reply
MK
9/5/2024 02:01:29 pm
It is interesting to note that a bulk paper storage is regarded as a deep-seated fire hazard in table 5.4.2.1 of NFPA 12.
Reply