Use Sprinklers In Lieu of 1-Hour Rated Glass?

5/8/2024

11 Comments

 
Can window sprinklers be used to protect internal glazing in partitions in lieu of fire rated glass partition?

The life safety engineer has requested to provide sprinklers on internal fully glazed partitions to save the cost of fire rated glazed partition. Not for the entire hospital, only some internal partitions in a hospital for glazing with 1-hour fire rated ones.

Although couldn't find anything in the NFPA 13 that support his request as I know this is valid only for atriums, am I right?

I appreciate the help and response as always.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
5/8/2024 08:17:59 am

Window sprinklers and wall ratings are available in NFPA 12- 2016 see 8.15.26.

There are a whole bag full of special requirements around using window sprinklers but they sure are cheaper than rated glass.

Make sure you follow all the cut sheet rules; Reliable and Tyco have several options for you.

To be super clear this is not an atrium water curtain, this is a specially listed sprinkler.

Reply
Jack Smeck
5/8/2024 08:42:15 am

Hi there,

I had a similar case recently. You are correct, this allowance is for atriums only (see https://www.meyerfire.com/blog/windows-sprinklers-fire-ratings-part-i).

However, there are manufacturers that have tested a window-sprinkler assembly to ASTM E119--the same standard used for testing fire rated barriers. This "assembly" includes specifications for the window in addition to spacing/location of the window sprinklers.

Tyco is the manufacturer I'm most familiar with (https://www.tyco-fire.com/products-and-solutions/sprinklers-nozzles-and-accessories/special-application/cws-ws_fis/models-cws-and-ws-sprinklers). As mentioned in the datasheet, since this isn't prescribed in the IBC, it needs to be submitted as an alternate means. Good luck!

Reply
Todd E Wyatt
5/8/2024 08:43:35 am

Per the scoping Code (e.g. IBC-2021) there are (3) methods for determining the fire-resistance rating (FRR) of building elements, components or assemblies including FRR glazing :

1. 703.2.1 Tested Assemblies
2. 703.2.2 Analytical Methods
3. 703.2.3 Approved Alternate Method

Based on the 703.2, the “703.2.2 Analytical Methods” is to be used “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” so this option is out.

That leaves “703.2.1 Tested Assemblies” or “703.2.3 Approved Alternate Method”.

FRR glazing shall be “tested in accordance with ASTM E119 or UL 263 and complying with the requirements of Section 707.” Section 707 addresses “Fire Barriers”. The ASPS “deluge system” exception for the “enclosure of atriums” is prescribed in IBC-2021 404.6 (see References below) and permits this as a substitute for the required 1-Hour Fire Barrier (1FB) separation of an atrium from adjacent spaces IF the atrium’s glass wall forms a Smoke Partition and it meets the (3) conditions listed.

If the life safety engineer can provide a tested assembly that includes an automatic sprinkler system (ASPS) with glazing meeting the requirements of the required FRR assembly, the AHJ may permit it.

However, many AHJs will not approve the substitution of a required (non-active) FRR assembly (e.g. 1-Hour Fire Barriers w/Fire Glazing protecting an Interior Exit Stairway) with an “active system” such as an ASPS. ASPS are not always 100% effective and some AHJs may use the intent of “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” per “703.2.2 Analytical Methods” against the requirements of “703.2.1 Tested Assemblies.”

Reply
Todd E Wyatt
5/8/2024 08:44:02 am

REFERENCES
IBC-2021
Chapter 7 Fire and Smoke Protection Features
Section 703 Fire-Resistance Ratings and Fire Tests
703.2 Fire Resistance
The fire-resistance rating of building elements, components or assemblies shall be determined in accordance with Section 703.2.1 or 703.2.2 without the use of automatic sprinklers or any other fire suppression system being incorporated, or in accordance with Section 703.2.3.

703.2.1 Tested Assemblies
A fire-resistance rating of building elements, components or assemblies shall be determined by the test procedures set forth in ASTM E119 or UL 263. The fire-resistance rating of penetrations and fire-resistant joint systems shall be determined in accordance with Sections 714 and 715, respectively.
703.2.3 Approved Alternate Method
The fire resistance of building elements, components or assemblies not complying with Section 703.2.1 or 703.2.2 shall be permitted to be established by an alternative protection method in accordance with Section 104.11.

703.4 Fire-Resistance-Rated Glazing
Fire-resistance-rated glazing, when tested in accordance with ASTM E119 or UL 263 and complying with the requirements of Section 707, shall be permitted. Fire-resistance-rated glazing shall bear a label marked in accordance with Table 716.1(1) issued by an agency and shall be permanently identified on the glazing.

Chapter 4 Special Detailed Requirements Based on Occupancy and Use
Section 404 Atriums
404.6 Enclosure of Atriums
Atrium spaces shall be separated from adjacent spaces by a 1-hour fire barrier constructed in accordance with Section 707 or a horizontal assembly constructed in accordance with Section 711, or both.
Exceptions:
A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
1. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;
2. The glass wall shall be installed in a gasketed frame in a manner that the framing system deflects without breaking (loading) the glass before the sprinkler system operates; and
3. Where glass doors are provided in the glass wall, they shall be either self-closing or automatic-closing.

Reply
Glenn Berger
5/8/2024 08:59:33 am

This is definitely accepted practice. You might be able to find some documentation in openings in rated construction and similar discussions.

Reply
Steve Cooper
5/8/2024 09:20:26 am

Check out ESR-2397. It is an evaluation report for two Tyco window sprinklers. Goes over how and when to use them. It also sites all the codes it is compliant with. It has the hydraulic requirements as well.

Reply
Jerry Clark
5/8/2024 09:26:44 am

Yes, you can. Now allowed in various applications, not just atriums. We employed this method of protection in 2-hour egress corridors for a large Google project:

https://icc-es.org/report-listing/esr-2397/

Reply
Brett
5/8/2024 09:58:44 am

Yes, you may use sprinklers to protect glass (glazing). There are a few companies who make window sprinklers. You will also find standard sprinklers used in older installations. There is also a Meyer Fire post on this: https://www.meyerfire.com/blog/windows-sprinklers-fire-ratings-part-i

NFPA 13 [2022 ed.]
9.3.15* Sprinkler-Protected Glazing.
Where sprinklers are used in combination with glazing as an alternative to a required fire-rated wall or window assembly, the sprinkler-protected assembly shall comply with the following:
(1) Sprinklers shall be listed as specific application window sprinklers unless the standard spray sprinklers are specifically permitted by the building code.
(2) Sprinklers shall be supplied by a wet pipe system.
(3) Glazing shall be heat-strengthened, tempered, or glass ceramic and shall be fixed.
(4) Where the assembly is required to be protected from both sides, sprinklers shall be installed on both sides of the glazing.
(5) The use of sprinkler-protected glazing shall be limited to non-load-bearing walls.
(6) The glazed assembly shall not have any horizontal members that would interfere with uniform distribution of water over the surface of the glazing, and there shall be no obstructions between sprinklers and glazing that would obstruct water distribution.
(7) The water supply duration for the design area that includes the window sprinklers shall not be less than the required rating of the assembly

19.3.5 Sprinkler-Protected Glazing.
Where the sprinkler-protected glazing is required to comply with 9.3.15, the water supply duration for the design area that includes the window sprinklers shall be not less than the required rating of the assembly.

19.3.5.1 For sprinkler-protected glazing, the number of sprinklers calculated for the glazing shall be the number in the length corresponding to the length parallel to the branch lines in the area determined by 28.2.4.2.

19.3.5.2 If a single fire can be expected to operate sprinklers for the sprinkler-protected glazing and within the design area of a hydraulically calculated system, the water supply to the sprinkler-protected glazing shall be added to the water demand of the hydraulic calculations and shall be balanced to the calculated area demand.

19.3.5.3 Hydraulic design calculations shall include a design area selected to include ceiling sprinklers adjacent to the sprinkler-protected glazing.

Reply
Dave
5/8/2024 10:42:23 am

Reliable has a good, archived webcast from Dec. 2020
https://youtu.be/VEX-pa9h4DQ?si=UuBdTVqET5y0nEM_

Reply
Franck
5/8/2024 12:54:08 pm

I would say yes if the windows are there and you need 1h rating.
I would say no for a new project, simply because a 1h rated wall, door or window is a passive protection. It works even if your fire protection system is impaired.
From an insurance point of view (property damage) it may make a big difference.
So for a new project, provide 1 h rated glass windows.

Reply
cathy
5/9/2024 10:48:33 pm

1, TYCO TY3388 window sprikler.
2, If there is pony wall below the glazing, that portion still needs to be fire rated.
3, I remembered the test was done for a glazing up to 4.2m high.
4, horizontal mullion would be an obstacle to change direction of the spray. Depends on the size and shape of the mullion, a second row of window sprinkler under the mullion may be needed.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT