Use Refill to Downsize a Water Storage Tank?

5/22/2023

15 Comments

 
This may sound like a strange question, but here it goes.

Is there a way to downsize a fire water storage tank based on the refill rate supplied by the city?

I know that in Houston there was a company that supplied calculations showing that the refill rate could supply the tank at a refill rate based on the flow test.

Could anyone substantiate this principle?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Anthony
5/22/2023 07:41:23 am

This is called a break tank. Ch 14.5 NFPA 22-2018 ed.

Reply
james evans
5/22/2023 08:28:32 am

I have designed break tanks, but this is a scenario where the city does not have the required flow and the tank is a static tank. In my case it is about 300,000 gallons if i cannot downsize it due to the city supply flow. A break tank is used when the city has enough flow but they want an air gap to insure no back siphonage.

Reply
SC
5/22/2023 06:05:00 pm

NFPA 22 standardizes the construction of fire protection water storage tanks for many purposes (including the tank water supply for a fire pump), defining a "break tank" as a tank providing suction to a fire pump whose capacity is less than the fire protection demand.

Here's the elephant in the room:
Can a break tank be sized less than the 15-minute duration of a fire pump operating at 150%of the rated capacity when calculating the tank Refill Mechanism (using a dependable water supply) as required by Chapter 14 (NFPA 22)?

Reply
Dan Wilder
5/22/2023 08:04:37 am

I've completed a couple over the years, not a break tank specifically, but an allowance to reduce the size of the main water tank based on available refill rates from the local water department.

We requested a letter from the water department (we did a flow test for the other) on available, worst case water refill to a tank (GPM IN), took the 150% demand from a fire pump (GPM OUT), and subtracted the two for actual usage. With AHJ approval, we had to prove at time of commissioning that everything worked as modeled...this was an exception due to space issues on the site more than a workable VE item.

ParkUSA is the company we last talked with about an actual Break Tank application (if that helps).

Reply
james evans
5/22/2023 08:30:53 am

Is there any place in code where this is allowed? I am not sure if it has been considered in water supplies for fire pumps. Yes the break tank concept is allowed but this is when the supply is sufficient.

Reply
Jesse
5/22/2023 08:07:40 am

I'm pretty familiar with the break tank requirement in Houston. And yes, you can consider the tank refill rate in your calcs. Not just for break tanks, but static supply tanks as well.

Reply
james evans
5/22/2023 08:32:24 am

Where in code is this allowed? I am more concerned with the static tanks, I have designed break tanks before.

Reply
sean
5/22/2023 11:14:26 am

The code does not restrict it. The code allows automatic water supplies and tanks. No where that i know of says you can't combine them.

Paul Pinigsi link
5/22/2023 08:08:54 am

Yes, we do then possible. It is essentially the same concept as a break tank. We have used this approach several times.

Reply
Glenn Berger
5/22/2023 08:12:27 am

I have done this in remote locations. Need to note, the reason that you have a water tank is that the city utility is unable to provide the required fire flow. Proceed with caution.

Reply
SCHULMAN
5/22/2023 08:34:32 am

Glenn's point is a good one ... Why do you have a tank if the city water is reliable enough to base calculations on? Yes, please proceed with caution especially if you are in an area where development is continuing as "city water refill rates" are subject to change / diminish over time. We don't count on "city power" when we are designing life-critical systems that require backup power as an example.

Reply
Casey Milhorn
5/22/2023 08:57:19 am

Yes, refill can be considered for storage tank size, as long as the source is deemed as a Reliable Automatic Refill. This is per NFPA 22.

Reply
Franck
5/22/2023 09:09:19 am

You're right saying that break tanks are normally used to create a "no connection zone" between city water supply and sprinkler system. The break tank is only used to be refilled by the city water at the rate the pump is taking water from it.

But as indicated above, your configuration is allowed as it is some kind of break tank anyway (but with a greater water capacity in your break tank).
When you are considering the refill rate to be sufficient to provide the duration (between the tank capacity + the refill capacity for the duration) with the pump operating at 150% as indicated by Dan, you have more than sufficient margin (no fire will require your fire pump to operate at 150% for the entire duration... otherwise you will be in an overtaxed system from the very first minute and this means that you won't be able to control the fire anyway).

But if you have no space limitation and if this is not an existing situation (i.e., existing tank but change of occupancy / hydr. calc. ends up with a higher demand), it would be better anyway to provide a dedicated tank of the dedicated size.
That way, if you have city water supply shortage (works on the city water mains, for example), you don't end up with an impairment on which you have no control.

Reply
Jay
5/22/2023 11:23:31 am

4.1.6 *
A tank shall be sized so that the net capacity plus automatic refill shall meet the system demand for the design duration, except as modified by Section 14.5 for break tanks

Reply
Alex
5/22/2023 04:18:38 pm

As others have mentioned, sizing is similar to a break tank.

The sizing of the tank is governed by the 2013 edition of NFPA 22.

Section 14.5.1(3) states that break tank shall be used to augment the city water supply when the volume of water from the city supply is inadequate for the fire protection demand.

Section 4.1.5 states that the size of the break tank shall be 150% of the rated capacity of the fire pump for a duration of 15-minutes.

When designing a break tank, also consider the required flow rate, the gallons per minute being supplied into the tank, and the tank's initial volume.

Thanks,
Alex

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT