Use QR & Residential in Same Compartment?

5/8/2025

8 Comments

 
Renovating an 11-story hotel using residential sprinklers in accordance with NFPA 13 (2019).

Calcs based upon S x L (4 sprinklers at .10 density) or manufacturer data sheets (which ever requires greater demand).

Sprinklers need to be 175° due to less than 24" from the side of the wall mount diffuser. There are a few rooms that require a SW throw of 20'-4" (22'-0' per data sheets). However, many manufacturers do not manufacturer this 22 ft throw in 175°, only 155°.

Can I use a quick response (Viking VK630) SW that throws 22 ft along with the residential sprinklers in the same compartment?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments
Pete H
5/8/2025 06:20:56 am

I don't see a specific code restriction in 2019 to prevent this (provided the residential head is quick/fast response, if the residential head is not quick/fast response, you've found a magical standard response residential head I've never heard of before.)

You're in 13, so you were going to do a 900-1500 square foot calc with all heads at least operating at .1 density as is, so it's not like there's a downside to the QR head because you're not going to be allowed to a 4-head residential calculation anyway... though similarly if you are that worried, there's not really a cost difference if your pendants are residential or just regular QR concealed in this application.

Reply
Ed T
5/8/2025 08:20:34 am

NFPA 13, 2019 12.1.4 states that if residential sprinklers are installed in a compartment, all sprinklers within the compartment shall be residential sprinklers

Reply
Jesse
5/8/2025 08:31:16 am

I would say no based upon 2019 NFPA 13 12.1.4

12.1.4

Where residential sprinklers are installed in a compartment as defined in 3.3.38, all sprinklers within the compartment shall be residential sprinklers.

So, unless the VK630 carries a residential listing, I don't think that would be acceptable.

Reply
Jonathan W.
5/8/2025 08:57:09 am

Aside from the code requirements, I believe it's important to understand Residential Sprinklers are designed differently and are tested to meet specific life safety criteria. This includes spray pattern, compartment tenability levels (oxygen, temperature, carbon monoxide), and response element. Residential Sprinklers are designed to wet the walls VS providing a water density at the floor level. They are designed to enhance the survivability within the room of origin compartment.

It would not be appropriate to substitute a non-residential sprinkler in this space unless the sprinkler is listed specifically for residential applications.

Reply
Casey Milhorn
5/8/2025 08:59:38 am

I would advise doing anything you can to get that separation and use that 155, otherwise you will need to use QR light hazard sprinklers, which then kicks you out of the 4 head design.

Reply
Jack G
5/8/2025 09:03:37 am

The sprinklers within a room must have the same response time so no. 2019 NFPA-13: 9.4.3.2.
So make them all Qr sprinklers and do a reduced design MRA per the chart ?
or residential sprinklers and do a 4 head MRA calculation ?
A 900 sq ft calc might be at least be 6 rooms. The area above for 2 rooms appears to be 28x 11.
Sprinkler flow within closets bathrooms if they fall into the MRA are required to be included in the calculations,
Would room design method or small room ( 800 sq ft) rule be a better design approach ? I would try room design— 1 room and add 2 heads in the corridor.
Is the shaft wall between the bathrooms fire rated? Requires a 15 minute thermal barrier.
How about common wall between the rooms?
All construction must meet/rated per the applicable code.,

Reply
Jose R Figueroa
5/8/2025 12:32:22 pm

155°F Quick response is acceptable. I don’t see any restriction in NFPA 13 2025.

Reply
O.P.
5/8/2025 02:30:51 pm

Thanks all for the responses - UPDATE - I missed NFPA 2019 12.1.4 that many had referenced - I mistakenly got caught up in 12.1.2 and A12.1.6.1- Interestingly enough, I also made the mistake of looking for a 5.8 or larger orifice SW to throw the 22 ft in 175° temp. I should not have limited my search by orifice. Viking residential SW VK486 9 4.0 k) throws 22 ft , 175° with less psi / gpm than the larger orifices. Todays lesson - slow down

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT