Use NFPA 13R for Apartments and Storage Area?

8/29/2024

7 Comments

 
I have a church reuse project with three apartments on the top floor and open storage on the lower/basement level.

Can I use NFPA 13R throughout?

Or, do I need to base it on an NFPA 13 system with a typical 4" riser?

​I believe the building is Type V-B construction. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
8/29/2024 06:48:46 am

My early morning take:
Is the open storage divided by the apartments where it's just their "basements" and part of their residences, a communal storage area that's open to all three resident tenants but no one else, is it going to be a commercially offered storage space or a storage space used by the building owner separate from the residences?

If the first one, there's an argument that it's just the basements of the apartments and still viewed as part of the residential space.

If any of the last three... even the communal storage one, I'm leaning on bottom floor is 13 and they need to give it adequate separation to make the top floor 13R. And they'll want to with V-B construction to avoid the expensive dry system the combustible construction above the roof would need in 13.

From the 13R handbook:

"Where buildings of mixed use can be totally separated so that the residential portion is considered a separate building under the local code, NFPA 13R can be used in the residential portion while NFPA 13 is used in the rest of the building. Examples of accessory occupancies found in NFPA 13R installations can include parking garages/areas, community laundry rooms, clubhouses, exercise facilities, tenant storage, and so forth."

So unless these are totally separated or the building is totally a residential occupancy, I'd say you are stuck in 13. But I can be completely incorrect.

Reply
Peter A
8/29/2024 08:11:58 am

I've got a landlord of a new 4 unit, that has separated "landlord storage" likely for his RV and landscaping business. I told him that he needs to install a 13 system, as the building is no longer considered an apartment building with tenant storage.

Reply
Todd E Wyatt
8/29/2024 08:25:28 am

Per the scoping Code (e.g. IBC-2021), the building, if classified as a Group R-2 Occupancy Classification (OC), NFPA 13R would be permitted :

903.3.1.2 NFPA 13R Sprinkler Systems
Automatic sprinkler systems in Group R occupancies shall be permitted to be installed throughout in accordance with NFPA 13R where the Group R occupancy meets all of the following conditions:
1. Four stories or fewer above grade plane.
2. The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.
The number of stories of Group R occupancies constructed in accordance with Sections 510.2 and 510.4 shall be measured from grade plane.

As Pete explains above, if the "basement” is classified as a Group S Storage w/a above Group R-2, the Group S Storage is req'd to be protected by an automatic sprinkler system (ASPS) per the following :

903.2.8 Group R
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided THROUGHOUT all buildings with a Group R fire area.

The Group S is req’d to be protected by a NFPA 13 ASPS.

The Group R-2 & Group S-2 can be separated into (2) separate FIRE AREAS …

901.7 Fire Areas
Where buildings, or portions thereof, are divided into fire areas so as not to exceed the limits established for requiring a fire protection system in accordance with this chapter, such fire areas shall be separated by fire walls constructed in accordance with Section 706, fire barriers constructed in accordance with Section 707, or HORIZONTAL ASSEMBLIES constructed in accordance with Section 711, or a combination thereof having a fire-resistance rating of not less than that determined in accordance with Section 707.3.10.

… HORIZONTALLY by a 2-Hour Horizontal Assembly (2HA) :

707.3.10 Fire Areas
The fire barriers, fire walls, horizontal assemblies or combinations thereof separating a single occupancy into different FIRE AREAS shall have a fire-resistance rating of not less than that indicated in Table 707.3.10. The fire barriers, fire walls, horizontal assemblies or combinations thereof separating fire areas of mixed occupancies shall have a fire-resistance rating of not less than the highest value indicated in Table 707.3.10 for the occupancies under consideration.

TABLE 707.3.10 FIRE-RESISTANCE-RATING REQUIREMENTS FOR FIRE BARRIERS, FIRE WALLS OR HORIZONTAL ASSEMBLIES BETWEEN FIRE AREAS
OCCUPANCY GROUP FIRE-RESISTANCE RATING (hours)
R & S-2 = 2 Hours

Reply
Dan Wilder
8/29/2024 08:22:48 am

At first I read 3 levels...but your question is 3 apartments on the top floor with open storage on the lower/basement level. With no information on number of stories above the FD access, total building height, allowances taken within the V-B construction for ratings/egress/floor area, or rated horizontal separations (to name a few) I would venture to say that the building will require a full 13 system.

https://www.meyerfire.com/blog/summary-of-differences-in-nfpa-13-13r-13d

https://www.meyerfire.com/uploads/1/6/0/7/16072416/meyerfire_-_sprinkler_-_nfpa_13r_13d_code_impacts__2021_.pdf

Reply
Glenn Berger
8/29/2024 08:35:46 am

Insufficient information provided to advise on question posed. Need a complete building description as the starting point.

Reply
Jack G
8/29/2024 10:39:42 am

According to the IBC and Meyerfire cheatsheet:
Section 503- if an allowed area increase- then an 13r system cannot be installed.
Table 508 ...separated occupancies: no 13r
Tables 601-- VA construction- no 13r however VB permitted a 13d if 2 stories.
708.3 ...: no 13r
For haz materials tables 307, highrise modificatuion 403.3, atriums 404 , unlimited area buildings 507, allowable area of buildings 704.8, nonresidential draftstops 717.3, other group draft stops no 13r, groups R-1 R-2 permited however sprinklers must be extended into the affected areas 717.r, manual fire alarm 907.2 yes 13r.
Balconies- mu@t be protected see 903.1.2.1.
Table 601
Off the top of my head, i run into a lot of projects that are erronieously classified 13r or 13d.
Remember ....how its built determines how its protected.

Reply
Jack G
8/29/2024 10:53:38 am

My answer to your question is since it’s a change of occupancy, and probably won’t meet the requirements I listed above for a 13r system,
You will need an NFPA 13 system.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT