Use K25.2 Sprinklers Up to 50-ft Roof Height?

2/17/2025

9 Comments

 
I have a requirement from a client to use K25.2 sprinklers on a building up to 50-ft in height.

The design criteria that is provided under NFPA 13 is 12 K25.2 sprinklers at 50 psi, but this criteria is not available in Chapter 13 of NFPA 13.

Does anyone know where this came from, or whether it's appropriate?

It's for up to a 50-ft roof for protection of cartoned, non-expanded Group A plastics. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Mark Fessenden
2/17/2025 08:05:04 am

It’s from FMDS 8-9.

Reply
Ed Dunn
2/17/2025 09:45:45 am

Try VK 514 K-28 Specific Application

Reply
Todd E Wyatt
2/17/2025 08:56:29 am

“K25.2” is referenced in Table 20.17.2.2.3 …

NFPA 13 - 2024
Chapter General Requirements for Storage
20.17* Protection of Idle Pallets.
20.17.2.2 Protection Criteria for Plastic Pallets Stored Indoors.
20.17.2.2.3
Protection with ESFR sprinklers shall be in accordance with the requirements of Table 20.17.2.2.3.
Table 20.17.2.2.3 ESFR Pendent Sprinkler Protection for Indoor Storage of Idle Plastic Pallets on Floor or Open Frame Racks

… and Table 25.6.3.1 :

NFPA 13 - 2024
Chapter 26 Protection of Rack Storage Using In-Rack Sprinklers
25.6 In-Rack Sprinkler Protection Options Independent of Ceiling-Level Sprinklers.
25.6.3 Hydraulic Design Requirements for In-Rack Sprinkler Protection Options.
25.6.3.1 In-Rack Sprinkler System Requirements.
Table 25.6.3.1 In-Rack Sprinkler System Design for Options 1, 2a, 2b, and 3

If either of these (2) references are not applicable to the Project, inquire why “K25.2” sprinklers are required.

Reply
Mike F
2/17/2025 09:34:12 am

Can the OP provide some more details?

Like what year standard of NFPA 13 is applicable? What is the storage arrangement that the prospective tenant will be using? Is this for a spec. Building or a design build project?


Reply
Jack G
2/17/2025 10:01:16 am

Yes FM 8-9, Vikings is approved to 55 feet, (9) sprinklers at 80 psi.
Always consult the manufacturers latest cut sheet as many 25.2 s are not.

Reply
Franck
2/17/2025 10:22:07 am

No, it's not appropriate.
For NFPA 13, it is 45 ft maximum (unless you add additional levels of EC in racks as per 25.7 - In-Rack Sprinkler Protection Options Independent of Ceiling-Level Sprinklers - from NFPA 13 Edition 2025).

This is not coming from FM 8-9 as well as it limits the height of building to 40 ft (with a demand of 9 K25 ESFR @ 40 psi for cartoned unexpanded plastic in racks).

As indicated by Ed Dunn, SPECIFIC APPLICATION ESFR PENDENT SPRINKLER VK514 (K28.0) can be used for building up to 50 ft, and is apparently FM approved for that purpose (even though not in DS 8-9), pending a strict respect of all the requirements provided in the data sheet from Viking.
These are K28 sprinklers (not K25) and 10 sprinklers at 40 psi are necessary per design.

But again, this is not an NFPA 13 requirement.
And this is pending AHJ approval.

Reply
Jose R Figueroa
2/17/2025 11:57:27 am

Frank & Dunn responses are correct. Please refer to FM DS8-9.
Additionally:
Viking News Letter

ESFR K-28 For 50 ft Storage without In-Racks
June 27th, 2019
FM Based on the recent successful fire test of 50-ft rack storage in single and double row racks with cartoned unexpanded Group A Plastics (and encapsulated/ unencapsulated Class I–IV commodities), FM Global approved a new type of ESFR sprinkler for high-challenge storage applications, the ESFR K-28. It is approved as a ceiling-only, quick-response, wet-pipe, pendent storage sprinkler.

FM Global previously listed ceiling heights for cartoned unexpanded plastics only up to max. 45 ft ceiling height (K-25.2). But this large K-factor ESFR sprinkler head can be used for rack storage and ceiling heights in excess of 45 ft (currently the limit in DS 8-9 July 2018) up to 55 ft without the need for in-rack sprinklers.

The FM fire test was performed in collaboration with Viking testing the company’s new ESFR sprinkler head and design, requiring 9 heads at 80 psi each (three sprinklers installed on three adjacent branch lines). The sprinkler installation design is based on FM Global’s DS 2-0.

The ESFR type head is listed to utilize a minimum aisle width of 8-ft for 50-ft storage. The total water demand for this ESFR system is approximately 2250 gpm and in line with similar type sprinkler systems and storage heights, and most likely will require the use of a fire pump. Hose Demand is 250 gpm per FM requirements.

Reply
Daniel Contreras
2/17/2025 04:11:56 pm

Jose,

The requirements came directly from the client, we have previously built a building form them under the same design criteria yet that building was 45ft. tall, I understand that with FM we might not have an issue.
In my research I found that the K28.0(VK5141) Viking sprinkler criteria for buildings up to 48ft, a design criteria for NFPA can be 12 K28.0 sprinklers @ 35 psi.. when I found it I presented the data sheet to the AHJ, I was working to solve a similar situation with a 50ft building height, he approved it to install it at 50ft.

I'll get in contact with the AHJ of this project to present the options we have to get a better clarification and requirement.

Thank you.

Joe Meyer (moderator)
2/17/2025 11:00:51 am

Just a friendly reminder for all comments - All comments are reviewed. Comments which do not contribute, are not relevant or are disrespectful in nature will be removed.

We built this forum to be a community where people can ask questions that need to be asked, and contributors can choose to help or not. We won't support commentary that's not in line with our goal of helping serve and improve the industry.

Thank you!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT