|
We're replacing old fire sprinkler systems in an existing warehouse in the mid-atlantic region with new ESFR systems.
The old warehouse house skylights every 25ft (which is a lot more than we see in new warehouses being built). No sprinklers are required in the skylights due to the size, however the number of skylights does raise questions about ceiling temperature. NFPA 13, 2016 Table 6.2.5.1 shows a maximum ambient ceiling temperature of 100°F for ordinary temperature sprinklers. It seems unlikely that the ceiling temperature would exceed 100°F in an occupied warehouse space (even on a hot summer day), so I'm thinking it make sense to install all ordinary temperature sprinklers (besides around unit heaters) to not delay sprinkler activation, but it looks like the newer editions of NFPA 13 allow of intermediate temperatures to be installed throughout warehouses. Is anyone seeing all intermediate temperature sprinklers installed in warehouse systems to prevent accidental discharge? NFPA 13, 2016-2025 all essentially say sprinkler temperature ratings for ESFR shall be ordinary unless Section 8.3.2 / 9.4.2 require intermediate- or high-temperature sprinklers. (Section 8.4.6.5 in 2016, 14.2.6 in 2019-22, 14.2.5 in 2025) Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
8/22/2025 08:18:30 am
1) Since the facility is existing, you can get temperature readings to support (or disprove) your position.
Reply
Anthony
8/22/2025 10:01:00 am
I agree with Glenn here. Also its August. Pick a hot day next week and see what the ceiling temp is. I'd expect something around ~110 later in the day. With that you're definitely justified for intermediate temp heads.
Reply
Brian M Gerdwagen FPE
8/22/2025 08:33:32 am
I have always put Intermediate Temperature sprinklers at warehouse ceilings. Most of the warehouses have been in SoCal and have recorded summer temperatures of 120F+. As for all the skylights, they may be combination skylight/smoke vents.
Reply
Dan Wilder
8/22/2025 08:42:22 am
That region has had several reoccurring heat waves yearly, with one recently in late June of this year (Boston hit +100°F). It would not be out of the question to install the intermediate temp ESFR sprinklers using that historical data.
Reply
Chad
8/22/2025 09:17:26 am
I’d have zero issue with all intermediate temps.
Reply
Jack G
8/22/2025 09:32:50 am
As Dan points out, intermediate temp heads are allowed, and temps could spike in the warehouse you described.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Aug '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
September 2026
PE PREP SERIES |
RSS Feed
