Use Fire-Rated Construction in lieu of Sprinklers?

10/31/2024

14 Comments

 
Is fire-rated construction ever enough to not warrant sprinkler protection?

Is there a NFPA 13 section that would validate this one way or another?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Brett
10/31/2024 06:28:40 am

Typically, no, but this is too vague of a question to give a straight answer to. The answer to your question will be found in your relevant building and or fire code.

NFPA 13 tells you how to design and install sprinkler systems. It does not tell you when a sprinkler system is required.

Reply
Jen McHale
10/31/2024 08:18:41 am

There is but only for electrical equipment rooms and there are specific criteria that need to be met (2 hour rated enclosure, no storage, dry electrical equipment only, etc). 2019 edition NFPA 13 9.2.6

Reply
franck
10/31/2024 08:22:51 am

And this is only as some regulations prohibit the presence of water pipes over electrical cabinets (at least at a certain distance)

Reply
franck
10/31/2024 08:21:07 am

It is definitely not in nfpa 13 as it is for the design of sprinkler systems, not for not the need of sprinklers

Answer may come from the Insurance company that may accept or not having no sprinkler protection.

But non combustible constructions is not the same purpose than sprinklers.
One is passive protection and the other is active protection
A non combustible construction does not prevent that everything can burn inside the building


This means that a combustible construction with nothing to burn inside requires sprinklers (to protect the building) and a non combustible construction may require sprinklers as well to protect the inside.

Reply
Glenn Berger
10/31/2024 08:21:51 am

Per the IBC, you can potentially avoid sprinklers with a more robust construction type. But this is based upon occupancy and other building parameters.

NFPA 13 provides details for the design, installation, testing and maintenance of sprinkler systems. It is very limited on where sprinklers may be omitted in an otherwise fully sprinklered building.

Reply
Adam
10/31/2024 08:22:09 am

I have been involved in projects in small towns where the water supply is inadequate to support a sprinkler system, but the Code may require one. This has either stopped projects entirely, or created conflicts between building owners and the AHJ.

I am aware of one instance in my area where an Architect has provided a robust fire-rated assembly in lieu of a sprinkler system, but this is a great risk. I know from speaking to the Architect that they were not at all comfortable providing that Alternative Solution.

A fire-rated assembly supposedly contains a fire to a set space for a minimum amount of time, but without intervention, it can be assumed that the entire space would be destroyed by the fire, and people could be trapped within. With a sprinkler system, there is a good chance that the fire will be extinguished, or at least controlled, in order to allow for people to leave the space, and maybe prevent complete loss of the space.

In my opinion, no amount of fire-rating is equivalent to a fully-functioning sprinkler system.

Reply
Greg
10/31/2024 09:41:09 am

Adam's post is similar to my thoughts and experience regarding rural locations. Alternates for sprinkler coverage seems to occur in Ag-related seed process and manufacturing, where building separation is used as a key provision for loss-control. Fire wall separations in low-hazard storage warehouses, Type II construction and in a few instances, the construction type of dryer-buildings is inherently fire resistive, Type I.

For some companies who operate in the Ag-seeds business, the installation smoke detection systems is cost-effective and used for improving life-safety and initial response from rural fire departments.

In nearly all cases where sprinkler decisions arise, the predominant factor is the availability of a meaningful underground water supply from the local water utility, and/or the distance to connect to water line service.

Reply
J.H.
10/31/2024 08:40:31 am

The answer is not in NFPA 13, and will depend on the local adopted Codes.
If NFPA 1 is adopted, you will find sprinkler requirements in NFPA 1, Chapter 13, Section 3.2, "Where Required".

Reply
Jay
10/31/2024 09:40:43 am

If you compartmentalize a building sufficiently into separate fire areas that are each less than that which requires a sprinkler system to be installed per the occupancy in the IFC, IBC, NFPA 1, then yes. Of course there are those occupancies that require a fire sprinkler system regardless of fire area such as residential.

Reply
Charles Riforgiate
10/31/2024 09:44:36 am

2018 IBC Section 901.7 Fire Areas
Where buildings, or portions thereof, are divided into fire areas so as not to exceed the limits established for requiring a fire protection system in accordance with this chapter, such fire areas shall be separated by fire walls constructed in accordance with section 706.

Fire wall construction is permitted to reduce the fire area of a building or structure beneath the fire sprinkler thresholds indicated in sections 903.2 through 903.2.12.

i.e. - Group F-1 requires fire sprinklers where the fire area exceeds 12,000 s.f. (proposed F-1 13,000 s.f. building)
Use fire wall construction to create "separate buildings" resulting in 2 fire areas - #1-9,000 s.f. - #2 - 4,000 s.f.

Reply
Mark Harris
10/31/2024 01:57:00 pm

All great comments. In smaller towns in IL I have seen 2 or 3 less than 12,000 SF metal buildings built with some separation and a corridor between buildings with rollup fire door at corridor entrance. Only reason I can imagine for that was to avoid fire sprinklers. And as noted above probably inadequate water supply.

Reply
Todd E Wyatt
10/31/2024 09:56:18 pm

SUMMARY
ASPS are not permitted to substitute for the minimum FRR of building elements, components or assemblies UNLESS an “alternative design” is submitted to the AHJ and they approve it (per IBC-2021 104.11).

EXPLANATION
The scoping Code (e.g. IBC-2021) identifies WHERE an automatic sprinkler system (ASPS) is required based on the Occupancy Classification(s) (OC) assigned to the building (Group R-2) and/or “Specific Building Areas and Hazards”, not the Type of Construction (TC) of the building.

The referenced ASPS standard (e.g. NFPA 13-2019 or NFPA 13R-2019) prescribes HOW a building’s/structure’s ASPS is to be designed, installed, inspected, and maintained.

The IBC-2021 includes “EXEMPT LOCATIONS” per 903.3.1.1.1 (7 exemptions) & 903.3.1.1.2 (1 exemption) … see REFERENCES below.

There are (3) methods for determining the fire-resistance rating (FRR) of building elements (including FRR for primary structure (e.g. columns)), components or assemblies:

1. 703.2.1 Tested Assemblies
2. 703.2.2 Analytical Methods
3. 703.2.3 Approved Alternate Method

Based on the 703.2, the “703.2.2 Analytical Methods” is to be used “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” so this option is out.

That leaves “703.2.1 Tested Assemblies” or “703.2.3 Approved Alternate Method”.

If the life safety engineer can provide a tested assembly that includes an automatic sprinkler system (ASPS) meeting the requirements of the required FRR assembly for the column, the AHJ may permit it.

However, many AHJs will NOT approve the substitution of a required passive FRR assembly (e.g. encasement, FRR membrane protection of a wall, or SFRM) with an “active system” such as an ASPS. ASPS are not always 100% effective and some AHJs may use the intent of “WITHOUT the use of automatic sprinklers or any other fire suppression system being incorporated” per “703.2.2 Analytical Methods” against the requirements of “703.2.1 Tested Assemblies.”

“Water curtains” are permitted to be substituted for fire-resistance rated (FRR) opening protectives in buildings protected throughout by an automated sprinkler system (ASPS) by the scoping Code (e.g. IBC-2021 705.8.2) if approved by the AHJ (e.g. Building Official).

Opening Protectives (OP) are (typically) required based on the Fire Separation Distance (FSD) between the Exterior Walls (EW) and adjacent building(s) and/or the property line(s). Other than the exception for Opening Protectives per 705.8.2, the 1-Hr Fire Barrier (1FB) protection of atrium (window) walls can be downgraded to a 1-Hr Smoke Barrier (1SB) if IBC-2021 404.6 (3) Exceptions are met. ASPS providers have tried to use this atrium ASPS exception as a substitution for other FRR assemblies. Only the AHJ can approve of these “alternative designs.”

REFERENCES
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3 Installation Requirements
903.3.1 Standards
903.3.1.1 NFPA 13 Sprinkler Systems
Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Sections 903.3.1.1.1 and 903.3.1.1.2.
903.3.1.1.1 Exempt Locations
1. Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from a room merely because it is damp, of fire-resistance-rated construction or contains electrical equipment.
2. A room where the application of water, or flame and water, constitutes a serious life or fire hazard.
3. A room or space where sprinklers are considered undesirable because of the nature of the contents, where approved by the fire code official.
4. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.
5. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.
6. Fire service access elevator machine rooms and machinery spaces.
7. Machine rooms, machinery spaces, control rooms and control spaces associated with occupant evacuation elevators designed in accordance with Section 3008.
903.3.1.1.2 Bathrooms
In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncom

Reply
Todd E Wyatt
10/31/2024 09:57:04 pm

903.3.1.1.2 Bathrooms
In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.

Reply
Todd E Wyatt
10/31/2024 09:58:17 pm

ASPS = automatic sprinkler system

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT