MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Use Fire Pump Test in Lieu of Flow Test for Calcs?

4/1/2026

17 Comments

 
Can a fire pump test report be used in place of a hydrant flow test?

For an existing building, a fire pump flow test has to be done annually. It should include all the information a hydrant flow test provides to perform a hydraulic calculation for an existing building modification.

Is there any code basis for taking this approach?

I have an AHJ that keeps pushing back on this approach for determining the water supply information.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
Pete H
4/1/2026 06:19:02 am

It depends on AHJ.

But in most AHJ's I have seen: yes, it is acceptable (provided the pump test is within a year).

The best code reference I can scrape up in five minutes of research is A4.2(4) and 4.2(4) and Chapter 5 of NFPA 13 (2025 Ed.)

Basically the code refers to flow test information as one of (undefined) possible "approved methods" of obtaining water supply information.

It is weird that a pump test is an approved method for 99% of AHJ's in the country and you found the 1%, but if you did find the pump characteristic information and have a hydrant flow test, you should be able to enter both into your calculation.

Reply
Dan Wilder
4/1/2026 07:47:49 am

Can it be used, yes as it is listed in Chapter 5 as an acceptable source and I to have used the info for submittals.

Is it an accurate representation of the water supply, no because there is a municipal water supply (assumed) providing flow and pressure. It will also only provide a finite GPM range based on the capacity of the fire pump and the PSI loss across that limited GPM segment. It is likely a more restrictive path and would provide a higher margin of safety however that doesn't translate as an acceptable water supply in some cases (or some people).

Reply
Glenn Berger
4/1/2026 08:09:19 am

If this was my project - A hydrant flow test and a pump test would be required.

Reply
Josh
4/1/2026 10:05:05 am

Ha, I always come to the forum posts to see "what does Glenn say?" because as an FPE, I find we speak a very similar language on most all issues, but you have more experience so there's insight in a lot of the comments.

Reply
Joe
4/1/2026 11:33:02 am

Would you also require excavation and mapping of the underground? As-builts are almost never available or accurate if they are.

In your pursuit of accuracy you are adding unknow variables.

Reply
Jose R Figueroa
4/1/2026 11:49:12 am

Joe, that's a tough requirement. I have done it occasionally during my days in Europe and Latin America. It always depended on the client or underwriter’s request for high-value or strategic occupancies. It's a pain in the neck to organize such an endeavor.

Josh
4/2/2026 09:21:25 am

this is a great point. Once NFPA 24 hits at the public, I've found the underground is rarely accurate. Aboveground being inaccurate where it can be traced visually is one thing, but the UG being who knows what is sometimes terrifying that nobody seems to know for sure!

Jesse
4/1/2026 08:11:32 am

I'm with Dan and Glenn here. It can be used, but if it were my project with my stamp on it, I would require a hydrant flow test.

Reply
Ivan Humberson
4/1/2026 08:25:06 am

IMHO, for an existing building, a flow test of a hydrant in the vicinity of the building is not as accurate as a fire pump test inside the building. The existing fire main supplying the building likely has corrosion and tuberculation that would change the hydraulic flow characteristics from what would be expected for new pipe. I maintain that, for an existing building, the only way to accurately know what the available water supply will be to the base of the sprinkler riser is to flow test the underground pipe. The fire pump flow test would be a good representation of that available supply. (Just don't forget to adjust for variations in the available supply based on the water purveyor's data.)

Reply
JI
4/1/2026 08:59:58 am

A fire pump would have far more accurate results than a hydrant flow test in my opinion. However, as you may be aware listed gauges are not calibrated or liquid filled so unless the inspector performing the test is replacing the gauges on the fire pump suction and discharge to be liquid filled and calibrated for the test, you can argue the results may not be as accurate. The pitot gauges being used to measure the flow would likely be liquid filled calibrated gauges.

In a perfect world you would get both a fire pump and hydrant flow test, however if I could only get one, I would want the fire pump flow test since it includes the data from the water supply and the fire pump performance which can degrade over time. Also, depending on the fire pump size, 6 hose valves with playpipes measuring the flow versus two hydrant butts, I will trust the fire pump test header. Realistically if you plot the suction side pressures against the pump flows you should get something close to the hydrant test, with the exception of the friction loss from the underground piping from the road to the building. I have performed this exercise when our fire pumps are commissioned with a full fire pump flow and the results are very close. On the last couple we have commissioned, our fire pump flow test is within 1 psi of our theoretical fire pump performance + the hydrant flow test.

In fact, I would argue there is usually extra safety factor since if we use a fire pump test curve, we have to start at the fire pump discharge flange. Therefore, all hose allowance must be applied at the discharge flange, rather than at the nearest hydrant or roadway connection to underground water main.

Reply
Jose R Figueroa
4/1/2026 10:34:47 am

In my days as a field engineer, I often used the nominal pump performance curve because sometimes conducting a pump flow test isn't possible for various reasons. I always took 10% of the nominal curve as a safety margin.

Reply
Taylor Jenkins
4/1/2026 10:42:44 am

While a hydrant flow test is an accurate representation of what is available in the municipal water main, a current fire pump test is far more accurate in showing you what you actually have coming into the building. Assuming that the pump test was performed correctly with new gauges, the results will indicate any losses in the suction line from the water main to the pump suction which you can't otherwise approximate accurately.

For instance, we had an existing building with a fire pump that had not been tested recently. A flow test was performed and showed plenty of water for the design task inside the building. Then, the pump test was performed only to find out that the suction line coming in from the street was obstructed to a point that dropped the suction to the pump below 20 PSI during the test.

We now require forward-flow tests on all existing systems before performing designs. I've had three recent projects where the available flow and pressure at the riser was far less than what the flow test indicated out in the street.

Reply
Joe Meyer
4/1/2026 10:45:30 am

Even without a fire pump, I've had this happen on a project too.

Water supply at the street was fine (what we expected). Static riser pressure was fine. Main drain test was what it was (initial acceptance testing).

But once we did the forward flow, we hardly had anything. Turned out the building's supply tap was only partially made and was 80%+ obstructed.

We would have never known had we not conducted the forward flow test.

Reply
Jesse
4/1/2026 02:31:16 pm

Joe I had a similar situation in my Loss Control days surveying a furniture warehouse in Denver. Completed the survey and got the flow test. When I put it all together and calc'd the AS systems with the pump, it wasn't working. It was hydraulically inadequate. The underwriter freaked out and was going to bail on the policy. Turns out that a month or 2 before my visit, utility work had been done and the local utility left a valve closed on the public side. This made the difference between hydraulic adaquecy and not. But we wouldn't have know if we didn't get the flow test.

danefre
4/1/2026 11:29:07 am

One of the reasons we were pushed to do hydrant flow tests on pump jobs is to include the outside hose allowance. Depending on the software, there are some creative ways to include that but it's still getting called out regularly. The outside hose allowance SHOULD affect the net pump curve logically.

Reply
Jack G
4/1/2026 05:31:58 pm

Calibrated gauges are required in the 3 states around me for fire pump tests and hydrant flow tests.
Yes. Fire pump test with calibrated gauges is acceptable.
All municipalities around me require a hydrant flow test also.
So combining the 2 should be easy, except paying for the hydrant flow tests.
( hydrant flow tests can indicate open, closed valves from when the fire pump test was made due to replacement/ upgrading water lines) example— shutting down a main feeding city mains feeding pumps -freeze ups, repairs, to multiple buildings - cutting the supply to pumps , could cavitate.)
I ve made myself rules thru the years—--
Before testing the pump ( pump on ) I test the city only to ensure the pump won’t be affected. 60% of the time there is a closed city valve).

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT