Use ESFR Sprinklers To Avoid In-Racks?

11/3/2026

10 Comments

 
I have a storage rack configuration that has been installed with a storage height of 20 ft and a ceiling height of 30 ft. The commodity is Group A expanded plastics in cartons. It is cardboard boxes with cushions and foams, and some are wrapped in cling wrap.

I am trying to determine whether in-rack sprinklers are required for this configuration.

I have been reviewing the CMDA, CMSA, and ESFR sprinkler protection options. It is currently installed in a system that is designed in OH2. However, I think this is not sufficient.

I believe there may be an opportunity to modify the system and use ceiling-only ESFR protection based on NFPA 13, Section 23.6.3, which specifies a demanding area of 12 sprinklers, consisting of four sprinklers on each of three branch lines. Based on Table 23.6.1, which addresses cartoned expanded plastics with a maximum storage height of 20 ft and a ceiling height of 30 ft- based on selecting an ESFR sprinkler K-factor and its corresponding minimum operating pressure, then calculate the required water demand for the 12 sprinklers?

​I would appreciate any clarification on whether I am interpreting these provisions correctly and whether this approach would be sufficient or if in-rack sprinklers are necessary.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
11/3/2026 06:30:17 am

You're reading it correctly, a 12 head esfr calc of either K14 or K16.8 esfr sprinklers (doing 50 or 35 psi per head as a minimum operating pressure respectively) is sufficient to void in-rack protection requirements as per the protection layout outlined in Table 23.6.1 (NFPA 13 2019 ed.) for a 30'-0" max ceiling height and 20'-0" max storage of cartoned expanded Group A plastics.

Reply
Jesse
11/3/2026 08:10:21 am

ESFR is intended for just this situation. Larger orifice ESFR sprinklers are easier to calculate due to the lower operating pressure. I've had several projects with non-expanded Group A where I was able to avoid a pump because I had a pretty robust water supply.

However, with the current system being OH2, I don't think you'll get there by "modifying" it. You're moving way more water with Suppression Mode sprinklers than you are at OH2. I'd lean to demo the existing system entirely

Reply
Mark Harris
11/3/2026 08:29:57 am

Agree with Jesse and Pete. You will probably need a fire pump and hopefully your existing underground supply is not 6". If it is you will probably need new larger.

Reply
Glenn Berger
11/3/2026 08:55:10 am

You have gotten some great advice. BTW, I hate working on storage facilities.

Reply
Streeter
11/3/2026 09:32:29 am

I do quite a few ESFR systems and have learned quite a few lessons from them along the way. Pay special attention to the orientation requirements for upright vs pendent as that is sometimes an issue when maintaining 18" deflector height from deck.

Also, the 3x rule becomes a 4x rule with ESFRs, as well as a few other fun things to pay attention to.

Reply
Dave
11/3/2026 03:28:28 pm

And if applicable (or employable), the changes in the 2025 edition NFPA 13 for ESFR, like sloped ceilings, obstructions, documentation.

Reply
danefre
11/3/2026 12:51:58 pm

Great advice above.

Retrofitting ESFR is quite the challenge. It's not just hydraulics that you have to consider.There is a chance that the building is not suitable for ESFR just based on structure, existing MEP etc.

You're very limited on spacing and branchline elevation. You won't find out if it's viable until you actually decide on the K-factor/orientation and lay out the system. Read through the obstruction rules!

Reply
Michael
11/3/2026 01:23:53 pm

Follow up question since I have not seen any of the replies commenting on whether OP's storage arrangement in question is on solid shelf racks or open racks: wouldn't OP need to confirm if the storage is an open-rack configuration per NFPA 13 (2025) 23.1.3 before determining that no in-rack sprinklers are required?

23.1.3
The ceiling design criteria for single-, double-, and multiple-row racks in this chapter shall be based on open-rack configurations as defined in 3.3.147.

23.1.3.1
ESFR sprinklers shall not be permitted to protect storage on solid shelf racks unless the solid shelf racks are protected with in-rack sprinklers in accordance with Chapter 25.

Reply
Nimal Tissa,wijetunga
11/3/2026 09:07:24 pm

Your commodity classification is Group A plastic expanded /non exposed as per NFPA 13.

In line with NFPA 13 -2025 edition, please look in to the following because ESFR Application has other restriction.
1) Maximum ceiling and corresponding storage height as per material with above commodity classification. Check this very seriously.
2) no open top containers.
3) no close shelving or racks allowed.
4) Roof slope is 2 to 12 or maximum of 2 to 14
5) Number of sprinklers operated differ from 12 sprinklers to 16 sprinklers in line with roof slope.
6) Better to consider k-28 as the k factor.

Please note if anybody wants sprinkler system as one of the fire protection in their buildings must be constructed according to the requirements of sprinklers design and this is specifically applicable to warehouses,storage facilities,Distribution centers,Logistic facilities .

Reply
Bjørn
11/4/2026 07:27:01 am

ESFR - don't forget the flue spaces !!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT