I have a project with a 40,000 sf refrigerated storage area with an exposed metal deck roof with steel joists. Roof is sloped; the low end is 29-ft floor to deck and the high end is 31-ft 8-in.
Can I use the sprinkler criteria of 30-ft max ceiling height for storage areas of this space that are below the roof, where it is 30 ft or less, and use different sprinkler criteria where the roof exceeds 30 ft? More specifically, do I need to use the maximum roof height for the sprinkler criteria of the entire space? My issue is that there is rack storage and palletized storage, and FMDS 8-9 does not have a ceiling-only solution for palletized storage with a ceiling height greater than 30 ft. Any insight is appreciated, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
8/6/2025 07:57:35 am
Yep -
Reply
Glenn Berger
8/6/2025 08:16:46 am
1) 29 foot roof height - The reference that Dan provides has additional criteria that must be met before you can utilized the decrease design parameters for a lower roof elevation. If you can comply with all of the regulations that go for it.
Reply
Anthony
8/8/2025 09:05:02 am
You could with a baffle, separate the 2 areas FM has language on baffel construction.
Reply