Is it permitted to install fire pump cables, from the controller panel to the motor, through a cable tray using armored cables, at a height of about 4 inches (10 cm) above the finished floor level?
Are there any code or standard requirements that affect this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Sean
7/31/2025 08:16:51 am
This sounds like an NEC (NFPA 70) Article 230 and Article 695 reference exploration, as I believe there are various factors.
Reply
Todd Wyatt
7/31/2025 08:29:42 am
The scoping Code (e.g. IBC-2024) references NFPA 20 Standard for the Installation of Stationary Pumps for Fire Protection as it pertains to Fire Pumps. NFPA 20 references NFPA 70 NATIONAL ELECTRICAL CODE Article 695 Fire Pumps. See REFERENCES below.
Reply
Todd Wyatt
7/31/2025 08:30:14 am
REFERENCES
Reply
Todd Wyatt
7/31/2025 08:30:45 am
REFERENCES
Reply
chad
7/31/2025 08:36:29 am
As an AHJ I would not accept any method not prescribed in 695.6.(D) (1)