|
Section 9.2.2 in NFPA 14 allows protection for a standpipe that is not in a stairway to be "the piping is enclosed in fire-rated construction with a rating equal to that of the enclosed fire-rated exit stairway."
In the Gypsum Association Manual WP 3910 for a chase wall with staggered studs has a rating of 2 hours. Does such a 2-hour rated chase meet the intent of NFPA 14 when the standpipe is not in the stair? Thank you for your feedback! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
3/28/2025 07:51:25 am
Possibly....for some projects we have dealt with in the past
Reply
3/28/2025 08:15:00 am
You can build an enclosure with this wall construction, but you cannot install the pipe within the wall because that would not provide the required 2-hour protection. The 2-hour rating of this wall is from one side of the wall to the other, not from one side of the wall to the interior of the wall.
Reply
Glenn Berger
3/28/2025 08:18:08 am
A 2-hour fire-rated chase can be constructed to meet the requirements in NFPA 14. Additional detailing will need to be completed to achieve compliance with the reference provided.
Reply
Adam
3/28/2025 08:42:43 am
In Ontario, fire-rated walls are based on the fire resistance of one side to the interior, but they need to be constructed with an equal rating on either side.
Reply
3/28/2025 08:47:32 am
I am not aware of any calculation that equates two layers of Type X gypsum board to a 2-hour fire-resistance rating. The listed endurance for 5/8" Type X gypsum board is 40 minutes, so 2 layers provides 80 minutes of protection. You could use thicker gypsum board, but the detail provided utilized 5/8"
Reply
Adam
3/28/2025 08:58:59 am
The Ontario Building Code describes the "component additive method" which takes into account the framing and any insulaton as well. This can bring you up to 115 minutes with insulation - just shy of 2-hours. In addition to this calculation, the OBC provides approved fire- and sound-rated assemblies in their supporting documentation. Many of these assemblies, rated for two hours include two layers of type-X. It's also not uncommon to find UL-listings that allow this (similar to the example in the OP). So while a calculation method might not bring you to two-hours, the right listing or documentation will allow it.
Tayyab
4/27/2026 07:59:34 am
Just want to understand, the logic that the assemblies has fire resistant rating from one side, is it just for SB-2 additive method assemblies?
Reply
Jack G
3/28/2025 10:27:57 am
It is my understanding that in fully sprinklered buildings a 1 hr enclosure is required, 4 or greater 2 hour.
Reply
Jesse
3/28/2025 11:21:38 am
The short answer is "yes".
Reply
Jeff Ayers
3/28/2025 11:57:51 am
The short answer is ACTUALLY NO. Because 2-hour shaft enclosures are typically only required for multiple stories and the wall type shown is for 1 level.
Reply
Todd E Wyatt
3/31/2025 10:06:33 am
The fire-resistance rating (FRR) of an Interior Exit Stairway (IES) should be determined by the Design Professional (e.g. Architect). The FRR of the IES is determined by both the number of stories it connects (1-Hour <4 stories or 2-Hours >4 stories) and the FRR of the Floor Assembly it penetrates :
Reply
Todd E Wyatt
4/3/2025 01:40:27 am
CORRECTION ...
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed
