We have an old server room. The server room is split into two side-by-side rooms separated by a wood stud wall with sheet rock covering. One server room side is approximately 15'x30'. The other side is approximately 30'x30'.
The ceiling is a 2 ' x2' square ceiling tile with insulation above. Above the ceiling is open to the warehouse. The floating floor is suspended approximately 12". Wires for the servers are under the floating floor resembles a bird's nest. The wires also protrude through all four walls at various locations, but mainly between the floating floor and the concrete floor. The old sprinkler system needs upgrading. We are thinking of a clean agent system, but the cost would be monumental. Moving the server room to a different location would also be cost-prohibitive. Both server rooms would require doors, walls, and ceiling modifications including rewiring all the server equipment for a clean agent system. We have a large amount of server equipment. Does anyone have fire protection system(s) suggestion? Does anyone have reference material for suggestions on installing different systems to provide to upper management? What is the best method for providing a cost estimate for various types of systems? Also, has anyone had luck with the misting system in server rooms? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
5/26/2025 08:31:10 am
Lots of issues here:
Reply
David Kendrick
5/26/2025 08:40:06 am
In addition to the other practical considerations, I would like to include the following:
Reply
franck
5/26/2025 08:48:55 am
Glenn raised very good points
Reply
Johannes
5/27/2025 12:20:34 am
Not sure if a shipbuilder could give a valid answer here, but is the installation of a 'Novec' Fire surpression system considerable? We planned to install an automatic Novec system for protection of two switchboard rooms on a ferry project some years ago but the building company went bancrupt...:-)
Reply
5/27/2025 01:01:04 am
If Clean agent system is not viable due to budget constraint, most ideal protection is using the water mist system. It will not damage the equipment
Reply
Mark Harris
5/27/2025 08:28:58 am
If the walls do not go floor to roof deck door fan test to prove room integrity is an issue. And halocarbon (Novec 1230 FK-5-1-12) needs a sealed room. Inert gas system like inergen IG-541 with a discharge test may be an option and location of agent cylinders is flexible.
Reply
Elliot
6/3/2025 10:35:54 am
FK5-1-12 would be the first option i go with. I just got a quote for $200,000USD for a 2000sqft server room, but that is a very small price to pay for lost data.
Reply
Jerry O
6/17/2025 10:12:28 pm
If budget constraints are a concern, I recommend considering a portable fire suppression system utilizing flame-sensitive detection tubing installed within the server rack. Additionally, installing a multi-criteria smoke detector inside the room can provide early warning in the event of suppression system failure. For an added layer of protection, a dry chemical portable fire extinguisher (PFE) should be positioned outside the server room as a first line of defense.
Reply