MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Two FDCs When Building Permiter(s) Over 900ft?

2/6/2025

14 Comments

 
In NFPA 14, Sections 7.12.2.2(2) (2019) or 10.7.2.2(2) (2024) state that a "minimum of two FDCs shall be provided for each zone for the following: (1)* High-rise buildings (2) Buildings or multiple attached buildings exceeding 900 ft (274.3 m) perimeter distance."

Neither edition defines "perimeter".

Is it measured where the building meets grade?

Should it account for all exterior walls?

Two building which share similar "A" length and "B" width dimensions can produce vastly different "perimeters" depending how they're measured. (See image below.)
Picture
Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Pete H
2/6/2025 06:34:45 am

In my opinion: If it's undefined, typically account for the more stringent requirement.

So yeah, all exterior walls.

Reply
Anthony
2/6/2025 12:31:21 pm

I agree with Pete as well. I wouldn't start measuring small architectural features but gross building features if over 900' then add an FDC.

Reply
Aaron Easter
2/6/2025 08:09:49 am

I agree with Pete. Also, I believe the purpose is related to both building size AND ease of access.

Reply
Glenn Berger
2/6/2025 08:21:35 am

The complete and organization of the requirement was significantly changed between the two versions.

I am guessing that your issue is with the arbitrary 900 feet perimeter distance requirement.

There is a write-up in Appendix A for both referenced statements. I do like how the Appendix does state that "redundant FDCs could be needed," instead of shall be provided.

Back to your question on how to measure the perimeter distance - The "U" shaped building has more perimeter distance and most likely has more exits and therefore requires more standpipes and then the redundant FDC would be required..

Reply
Dan Wilder
2/6/2025 08:26:22 am

When not defined, common definition within Webster's is the next resource (Section 3.1) and see the bottom.

Intent - Where else is it defined in that standard (hopefully) but this one is vague...NFPA 1 assigns "Net Floor Area" as "...the inside perimeter of the outside walls..." which leads me to think to follow the total exterior wall length or the longer of the two options.

Even this is a little confusing because 1 & 2 differ enough to apply to both of your options.
perimeter
noun
pe·​rim·​e·​ter pə-ˈri-mə-tər
Synonyms of perimeter
1a: the boundary of a closed plane figure
b: the length of a perimeter
2: a line or strip bounding or protecting an area
3: outer limits —often used in plural
4: the part of a basketball court outside the three-point line

Reply
J.H.
2/6/2025 08:38:14 am

This requirement is driven by fire department access requirements, which is described in the Fire Code to be measured as follows:

NFPA 1:18.2.3.2.2 ...[A]ny portion of the facility or any portion of an exterior wall of the first story of the building...as measured by an approved route around the exterior of the building or facility."(2021 Ed.)

NFPA 14:7.12.2.2* Two fire department connections shall be provided for each zone, located either on opposite corners of the buildings where fire department apparatus access is provided or,
where not possible, physically separated to the greatest extent
possible for the following:
(1) High-rise buildings
(2) Buildings or multiple attached buildings exceeding 900 ft.
(274.3 m) perimeter distance

NFPA 14:A.7.12.2.2 For larger buildings, redundant fire department connections could be needed. Connections can be compromised by parked vehicles, damaged hose threads, debris in the intake piping, and other conditions such as falling debris from a fire above.
When a large campus-style facility is served by private fire
service mains that feed the standpipe systems, and the campus
covers a large area, additional fire department connections
could be provided at strategic locations to enhance the fire
department’s ability to pump to the system.

If you truly need a definition for the word "perimeter", then check which Code-adopted dictionary needs to be referenced.
NFPA 1:2.3.23 (2021 Ed.) references the "Merriam-Webster Collegiate Dictionary, 11th Edition."

Reply
Chad
2/6/2025 09:47:51 am

Check with the FD.... they may not want more than one. We very occasionally will have two if its more than a full city block or massive building but they are not always necessary.

Reply
Jack G
2/6/2025 11:22:41 am

Meyer Fire has an fdc cheat sheet that is applicable here and gives the code references and paragraphs.
In it they indicate building or multiple buildings were the perimeter exceeds 900 feet. The code references are from NFPA 14, so one would assume “ standpipe box “ would need to be checked.
From the diagram above the space between the two looks like an alley and not a street . In fact streets or parking lots or hydrants are not shown.
Hydrants would need to be within 100 feet per the city of Philadelphia ( to fdc) IBC standards references section 912 only indicate accessibility.
Of course the fdc s should be on a street. If ann fdc s are on rear or opposite ends signage with 6 inch letters apply.
For the example above I would install 2 each and on the signage I would identify the building/ and systems as they are in close proximity.
If a street— the paving is probably rated for the large heavy fire trucks.
If a parking lot the fire department access must be rated for the truck access also.

Reply
Todd E Wyatt
2/6/2025 12:14:22 pm

The scoping Code (e.g. IBC-2021) includes other FDC requirements (Section 912) but none regarding how to determine the number of FDCs.

IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 912 FIRE DEPARTMENT CONNECTIONS
912.1 Installation
912.2 Location
912.2.1 Visible Location
912.2.2 Existing Buildings
912.3 Fire Hose Threads
912.4 Access
912.4.1 Locking Fire Department Connection Caps
912.4.2 Clear Space Around Connections
912.4.3 Physical Protection
912.5 Signs
912.6 Backflow Protection

Reply
Sergei Gluhushkin
2/12/2025 11:22:21 am

How should the multiple Siamese be connected to the header?
If at some point they are connected together and then only one main connected to the header, then if piping in one is damaged, both will be unusable. So both need to be connected all the way back to the header.

Reply
Jon Bernal
2/12/2025 03:17:08 pm

Since the FDC feeds the fire pump, does that mean now this new FDC 900+ feet away needs to be pipped all the back to the pump?

Reply
Sergei G
2/14/2025 08:13:59 pm

NFPA 20 does not allow Siamese connections on the Suction side of the pumps

Reply
Andrew Almazan
2/28/2025 08:09:41 am

The FDC does not feed the fire pump. NFPA 13: 16.12.5.9 Fire department connections shall not be connected on the suction side of fire pumps.

Reply
Andrew
2/16/2025 03:58:08 am

Another weird clash between 13 and 14, one that neglects urban versus suburban applications, and that moves towards a design spec.

Remote FDCs have a very specific purpose for high rises. Makes little sense for low rise structures (and in some cases could be downright ridiculous). I'm familiar with many large footprint 3-4 story projects with standpipes (education)...never seen this rule applied.

Buildings that, shouldn't even have standpipes in a day when no FD is ever going connect to an outlet at a third floor open stair when they have hundreds of feet of preconnect, but I digress.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT