How would you go about designing for a trapeze supporting (2 or more) 6" mains over large spans?
For example, you have a 16'-0" trapeze span, your truss is every 8'-0". Your idea is to place one long trapeze across 16'-0" to support 2-4 feed mains treeing from a riser manifold. NFPA 13 says we double the section modulus for every pipe, but that is assuming the we are using (2) attachment points; it doesn't seem to explain different configurations like attaching at 3 or more points on the structure. How would we go about designing for this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
5/13/2025 08:43:45 am
This would be outside of NFPA's scope so a structural engineer would need to be involved.
Reply
COLIN
5/13/2025 10:31:40 am
If it's a hanger configuration not covered in NFPA 13, then it needs to be designed by an Engineer to meet the requirements of NFPA 13. Those are the only two options.
Reply
Anthony
5/15/2025 07:26:22 am
As others have said you'll need a structural engineer. If this is for a new build your project will have a structural engineer attached to it and it should be relatively straightforward to request support for your required design. If this is an existing building and a standalone sprinkler project you'll need to retain an engineer/firm. This sounds a lot more annoying than it actually is, could be a little pricy but the only legal way to go about non prescriptive design.
Reply