MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Tie Tenant Duct-Detectors to Building Fire Alarm?

10/27/2025

6 Comments

 
Good morning, I am in Florida and use the Florida Fire Prevention Code 8th Edition, which references NFPA 1 and 101 (2021), NFPA 72 (2019), NFPA 96 (2021), and NFPA 17A (2021).

I have a mixed occupancy strip mall that is fully sprinklered and has a fire alarm that was initially installed to monitor the sprinklers only.

One tenant upgraded the panel to accommodate a full fire alarm for their unit.

A different tenant, mercantile class C, in the strip mall has installed a hood and hood suppression system along with duct detectors for their upgraded AC system. The ducts serve only their unit and do not cross demising walls or serve other units.

My interpretation is that the duct detectors and hood suppression systems must be tied into the building's fire alarm.

Is this correct?

Another question, would this tenant then need to upgrade their unit to include pulls and notification appliances?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Chad
10/27/2025 07:25:52 am

The hood system has to be monitored by the fire alarm.

2024 NFPA 101 9.8.2.2
The actuation of an extinguishing system that is not installed in lieu of a required, supervised automatic sprinkler system shall be indicated at the building fire alarm system, where provided.


2022 72.17.14* Detection of Operation of Other Automatic Extinguishing Systems.

The operation of fire extinguishing systems or suppression systems shall initiate an alarm signal by alarm-initiating devices installed in accordance with their individual listings.


Duct smokes as well, 90A:
11.4.4.2


In addition to the requirements of 11.4.3, where an approved fire alarm system is installed in a building, the smoke detectors required by the provisions of Section 11.4 shall be connected to the fire alarm system in accordance with the requirements of NFPA 72.
'
They do not have to be fire alarm devices though. They can be supervisory. And for a sprinkled strip mall, IMO they should be supervisory. If it was an I, E, H or other critical B occupancy, then fire alarm.

Reply
Glenn Berger
10/27/2025 09:28:19 am

Total agreement with Chad. I was involved with the duct detector issue with USACE last week for a project in Alaska.

Reply
Ricardo Gonzales
10/27/2025 11:04:35 am

I disagree with the above gentlemen. 1st. The building has a sprinkler monitoring system is it not a Fire Alarm System.

The tenant installed a kitchen hood that is not required to be monitored if a Fire Alarm system is not installed. One isn't. The same goes for the Duct Detectors. IF a Fire Alarm system is installed.

This is the line where often others call a 'Sprinkler Monitoring System' a 'Fire Alarm System'. They are different. Now IF it's being classified as a Fire Alarm System by the AHJ, note that full notification will need to be installed throughout the building. i.e. tripling the cost to the client and the building owner. A fire alarm system provides full notification for the tenants, and a sprinkler monitoring system only provides the one outside for the FD.

Reply
Robert Morgan
10/27/2025 01:05:46 pm

I agree with Mr. Gonzales here,
This is a specific function fire alarm system only designed to monitor the sprinkler system. The hood suppression and duct detectors in a single tenant should not require monitoring by the sprinkler monitoring FA. If a tenant (like a daycare center) which required a fully compliant NFPA 72 FA system were to take a space or more, that tenant would have to have proper notification and activation appliances and would need to be monitored by the "building alarm" in that a flow anywhere in the strip would trip that units devices.

Reply
Chad
10/27/2025 01:54:03 pm

From the OP" One tenant upgraded the panel to accommodate a full fire alarm for their unit."

Although it might have been voluntary and only offer partial, once you add notification devices, their is implied protection and it needs to be connected. I doubt there is a true fire separation in there. This may vary from AHJ to AHJ but is readily enforceable.


Plus AHJ can always pull the because I said so card with:
4.4.4* Occupant Notification.


In every building or structure of such size, arrangement, or occupancy that a fire itself could not provide adequate occupant warning, fire alarm systems shall be provided where necessary to warn occupants of the existence of fire.


Reply
Jim (OP)
10/29/2025 10:18:38 am

Thank you all for the insight and a lot to chew on. I appreciate all of the expertise! This is a great forum.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT