MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Tie Duct Detectors to Sprinkler Monitoring Panel?

11/26/2025

6 Comments

 
We are completing a buildout for a spec suite; the shell warehouse building was just constructed and has a fire sprinkler supervising panel.

The fire department is saying we have to tie the duct detector into the fire alarm panel. This building does not have fire alarm, only sprinkler monitoring.

Are they correct in saying we have to tie in the duct detector?

Thank you!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

6 Comments
Brett
11/26/2025 08:18:10 am

Short answer - it's open to what the AHJ interprets
"fire alarm system" to mean across multiple documents.

Long answer:

The sprinkler monitoring system is defined in NFPA 72 as a dedicated function fire alarm system so it is not a building fire alarm system as you pointed out.

NFPA 90A requires duct detectors to monitored if the building has an approved fire alarm system. To me, this means building fire alarm system and not just a dedicated function fire alarm system but it isn't spelled out explicitly like that.

IBC/IFC 907.3.1 requires duct smoke detectors to be monitored, but with two exceptions (summarized below - not copied word for word):

1. Supervisory signal is not required if the duct detector activates fire alarm notification in the building.
2. If there is no fire alarm system, the duct detector has to activate a visible and audible signal in an approved location.

The IBC/IFC defines fire alarm system differently than NFPA 72 does, so this is again open to interpretation. My interpretation is that it means building fire alarm system as defined in NFPA 72, but your AHJ may interpret it differently.

So, the IBC/IFC will most likely be the driving factor here since at minimum a visible/audible signal is required in an approved location and don't forget that "approved" is also a defined IBC/IFC term.

I work for a fire sprinkler / alarm contractor and we include monitoring of duct detectors when we do sprinkler monitoring systems. There is a strong argument for local visible/audible signal only but it's simply not worth the argument from our perspective.


Reply
Glenn Berger
11/26/2025 08:26:33 am

Concur with Brett's response.

You may want to check the archives here -- I think that there was a very similar question asked recently.

Reply
Scott McCormick
11/26/2025 08:32:26 am

If in an I Codes town, they are wrong. A fire sprinkler monitoring system is Not a Fire Alarm System. The Code States, "Duct Detectors Must Be Tied into the Building Fire Alarm SYSTEM" Fire sprinkler monitoring is a dedicated system and not a fire alarm system

Reply
Paul Pinigis link
11/26/2025 08:40:20 am

While it’s a reasonable idea, it’s not a code requirement. Since you done have a fire alarm system, you don’t have to tie accessory monitoring into anything.

Reply
chad
11/26/2025 09:10:15 am

This one is a bit of a gray area

2019 NFPA 72

23.3.3.2* Dedicated Function Fire Alarm Systems.
23.3.3.2.1

In facilities without a building fire alarm system, a dedicated function fire alarm system shall be permitted and shall not be required to include other functions or features of a building fire alarm system.


This section strongly infers that you do not, but does not call out duct smokes specifically.


23.8.2.3

Where the building is not served by a building fire alarm system, independent dedicated function fire alarm systems and/or releasing fire alarm systems shall not be required to be
interconnected to function as a single system.

This section specifically excluded releasing panels.




But I also agree its AHJ interpretation. And its worth doing, IMO.

Reply
Greg Collier
12/3/2025 10:26:00 am

They should be saying that the Duct detectors will require audible supervisory signal at a constantly attended location.

We sometimes (usually) see them supervised by the FACU or the FACP rather than installing the visible and an audible signal in an approved location referenced in exception #2

With that said, a bit of wire and programed supervisory signal is pretty easy...


IBC 2021 - 907.3.1 Duct smoke detectors.

Excerpt:

Activation of a duct smoke detector shall initiate a visible and audible supervisory signal at a constantly attended location and shall perform the intended fire safety function in accordance with this code and the International Mechanical Code. In facilities that are required to be monitored by a supervising station, duct smoke detectors shall report only as a supervisory signal and not as a fire alarm.


Exceptions:

1.The supervisory signal at a constantly attended location is not required where duct smoke detectors activate the building's alarm notification appliances.

2.In occupancies not required to be equipped with a fire alarm system, actuation of a smoke detector shall activate a visible and an audible signal in an approved location. Smoke detector trouble conditions shall activate a visible or audible signal in an approved location and shall be identified as air duct detector trouble.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT