MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Three Buildings Under One PIV and One FDC?

6/12/2025

10 Comments

 
Our project is a school campus with nine buildings.

The Civil Engineer has designed the underground so that three buildings are controlled from a single PIV and an FDC. Additionally, they want butterfly valves on each fire sprinkler riser.

Does shutting off three buildings become an issue, and is this within the NFPA 13 parameters to dictate this one way or another?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Glenn Berger
6/12/2025 08:11:02 am

Please tell me that these 3 buildings are attached and may look like a single entity from a site plan.

Someone else will weigh in on NFPA specifics, and also ask which versions of codes that the design is based upon.

IMO, this is just wrong.

Reply
Chad
6/12/2025 08:29:22 am

Get the FD/AHJ to weigh in and tell the engineer what they will need for an FDC if they are really separate buildings not just looks like it as Glenn said. It’s the AHJ’s call not the PE.

Valves on risers, not the FDC, is fine as long as it’s supervised.

I’m sure someone else will throw up references.

Reply
Ryan Grant
6/12/2025 08:29:26 am

From an AHJ perspective, I would separate PIVs and FDCs for each building in case you need to shut down the system for any reason, which would require a fire watch for all three buildings. This could be a greater expense to the owner vs the additional PIVs and FDCs.

Reply
MOHAMMAD MASHIRUL HAQUE
6/12/2025 08:42:17 am

I had a project in a residential community where we designed a free-standing alarm check valve assembly with a fire department connection (FDC) located near the fire apparatus access road. For each building, we had a provision for a zone control valve assembly. This type of arrangement could be in compliance with NFPA 13 (2019) as follows:
1. The maximum system protection area considered for light hazard is 4830 sq.m, as per NFPA 13 (2019), Section 4.5.1.
2. As per NFPA 13 (2019), Section 16.9.11.3: “The floor control valve, check valve, main drain valve, and flow switch required by 16.9.11.1 shall not be required where the total area of the floor combined does not exceed the system protection area limitation.”
3. As per NFPA 13 (2019), Section 4.5.6.2: When acceptable to the Authority Having Jurisdiction (AHJ), detached structures shall be permitted to be supplied by the fire sprinkler system of an adjacent building.
AHJ Concern – Why would an authority having jurisdiction have concerns about multiple buildings using the same fire sprinkler system? From the standpoint of an AHJ, the primary problem occurs if each building is or becomes owned by different owners. If the source building owner stops maintaining the water supply and the buildings are under separate ownership, it becomes very difficult to enforce fire code maintenance requirements for the dependent buildings. If the AHJ allows the use of the exception in Section 4.5.6.2, it should be only in situations where it is unlikely or impossible for the ownership of the individual buildings to split, or where legal easements are recorded.
4. A free-standing alarm check valve assembly shall have an OS&Y gate valve, alarm check valve, gauges, retard chamber, tamper switch, flow switch, pressure switch, water motor gong, test and drain valve, drain connection, etc., and shall be equipped with a two-way FDC with a check valve facing toward the fire apparatus access road. This arrangement shall serve a combination of three accommodation buildings, where the total area does not exceed the maximum limitation for light hazard occupancy.
5. Each building shall have a dedicated zone control valve assembly, consisting of a butterfly valve with supervisory switch, check valve, pressure gauge, inspector’s test and drain valve, and flow switch, in order to integrate each building with the fire alarm system allowing the status of each building to be monitored individually and isolated for maintenance individually.

Reply
Jesse
6/12/2025 08:42:47 am

I'm curious as to whether there are hydrants on the underground system. If so, I imagine each hydrants has an NRS valve.

I don't necessarily with the single PIV, as its not acting as a sprinkler control valv. The butterflfy valves are. I had a project with a lot of underground feeding 3 or 4 buildings and some hydrants. The AHJ didn't really care about PIVs, they just wanted keybox valves. All of the AS risers had butterfly valves. My point being, see what the AHJ wants

Reply
Paul Pinigis link
6/12/2025 08:49:52 am

First, you need to confirm that these are three separate "buildings" and not just three separate "structures". Review the building code analysis for the project.

Reply
Louie Lincoln
6/12/2025 09:22:09 am

If the valve in 1 building is closed then that building has no FDC.

Reply
Anthony
6/12/2025 09:53:43 am

I don't think you have code compliance here. Separate buildings should have separate control valves and FDC's.

Is this a case where say on a campus the buildings are touching or connected but coded as "separate buildings" in this instance I could see this being plausible.

Reply
Jack G
6/12/2025 11:32:11 am

For my money, I would not install this as described above.
First of all, I would install a PIV for each lead in.
Each riser should have its own FDC, Labeled for area it services.
If there are hydrants off the underground so they are near the fdc s , I would have a fire service valve, or a meter pit with BFP, Meter, Check valve , and an fdc( common) if AHJ agrees

Reply
Streeter
6/12/2025 02:03:48 pm

It is very unlikely that these FDCs are piped correctly. NFPA 13 (2025) 16.12.5.1 says that FDC piping needs to be connected to the system side of the water supply check valve if it is a single zone system.

It there are multiple systems in a single building, it is permitted to be piped between the supply valve and system control valves.

From what I gather on the question, you have three buildings each with an individual riser. The only way this might be compliant is if the AHJ approves the location for a remote FDC that is connected underground to the building system piping (Figure A.16.12.5.5(a)) after a system control valve and check valve (both of which need to be in an accessible pit for maintenance.) And the FDC check valve needs to be in an accessible pit for maintenance (Figure A.16.9.5)

I would also say that there should be clear signage on the FDC as to what buildings/zones that FDC feeds.

The ways to not have the Civil Engineer do this is to contact the AHJ, who should require FDCs on each building per their discretion per section 16.12.5.7, or to reference 16.12.5.1 which says the FDC should be on the system side of piping, the whole purpose of which is so no valve has the ability to stop the FDC from supplementing any sprinkler system., even in the worst case of the riser valve or any other upstream valve being off at the time of a fire.

You could also consult just about any other FPE and they will tell Civil just about the same as above for you.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT