MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Standpipe Locations with Many Horizontal Exits?

4/8/2026

8 Comments

 
I'm working on a fire protection design for a new apartment building. The architect is adding what they're calling horizontal exits throughout the building, which will increase the number of required standpipes per the local building code (IBC-based, 2025) Section 905.4.

Per the exception to 905.4.2, I do not believe we will need hose connections on both sides of every horizontal exit within the building. I think additional standpipes and hose connections will only be required in the center of the building.

Other than the egress stairwells, where are standpipes and hose connections required to be located?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments
Dan Wilder
4/8/2026 07:58:15 am

Looking at the exception for this section, no additional hose valves (or suppling standpipes) would be needed for any of the doors within 100' of the exit stairwells.

Doing the math on my fingers (sorry, leaving the shoes on), it looks like you'll only need an additional hose valve in the center where the black text is located (CIR - 1,000 SF). Possible omitted all together if the door can be opened and the 30' of hose stream can be applied. Now how that ties into the distance to the end of the units would be another possible reason the center hose valve may be needed.

This also depends on the hose valve location within the stairwell (main or intermediate landing) and if your AHJ requires the distance to start at the hose valve or just at the door per your sketch.

Reply
Glenn Berger
4/8/2026 08:15:00 am

There is a problem with the horizontal exit concept. There is a provision that the maximum number of horizontal exits is 50% from any given spot (or similar language).

Reply
Jim Grostick
4/8/2026 08:22:58 am

Good points on the distance math. One thing worth flagging from an operational standpoint: firefighters are trained to follow their hose line back to safety when conditions deteriorate. If that line leads to a mid-corridor standpipe connection instead of a protected stairwell, they’re retreating to an unprotected space — which is a real problem in a fast-moving fire.

Modern standpipe kit operations are also typically anchored out of the stairwell on the floor below, advancing up through the stairwell door. A center-hallway connection disrupts that model.

In our jurisdiction we require hose connections in every stairwell, including rooftop access — so the stairwell is always the operational anchor point regardless of how the horizontal exits are laid out.

So even where the code exception lets you skip the center valve on distance alone, it’s worth a conversation with the AHJ about whether stairwell valve placement can be optimized to cover the building without putting a hose connection in the middle of an open corridor.

Code minimum and operationally safe don’t always line up — this feels like one of those cases.

Reply
Laura L Henning
4/8/2026 08:57:55 am

That's a lot of horizontal cross corridors duel swings. First question is are they all horizontal egress walls, or are they IBC 706 fire walls for area separation, smoke barrier walls for smoke compartment or a rated fire barrier? Egress codes require at least 50% or more exits in a horizontal egress to exit to the outside or a stairwell opening directly to the outside. in theory only one set can be a horizontal exit, but the others could be fire walls or smoke barriers.

If the IFC is enforced, section 504 gives the local fire department the option to state where they want them. Most departments want one on each side (if required) if it is a Smoke Barrier. but every department is different.

Reply
Todd Wyatt
4/8/2026 09:15:32 am

Horizontal Exits (HE) in this residential application are typically added to a story based on the Exit Access Travel Distance (EATD) to the (2) Exits … the (2) Interior Exit Stairways (IES) … exceeding the maximum 250-FT for R-2 that is protected by an automatic sprinkler system (ASPS) per the scoping Code (e.g. IBC-2024 TABLE 1017.2).

To check this 250-FT maximum EATD compliance, these are the following steps …
1. Determine the Travel Distance (TD) between the (2) IES (+/- 215 FT),
2. Determine the hallway point (+/- 108 FT),
3. Determine the Most Remote Location (MRL) from this hallway point to the (2) IES.

Based on my scaled calculations, the Most Remote Location (MRL) from both IES is +/- 147 FT which is below the maximum EATD of 250 FT. A HE is NOT required to meet the EATD.

The Building Area (BA) for this Story is +/- 15000 SF which would have a calculated Occupant Load (OL) of between (75) to (90) Occupants. The Means of Egress capacity of the (2) IES can accommodate this OL so a HE is NOT required to meet Means of Egress capacity.

The HE may be a “result” of adding a Fire Wall (FW) to separate the story into (2) separate buildings to meet Allowable Building Area to meet IBC Table 506.2. However, a R-2 protected by an ASPS includes Allowable Areas that exceed 15000 SF based on all Types of Construction so a FW would not be required.

I recommend requesting the reason for the addition of the HEs and challenge them if it (or they) complies with IBC Section 1026 Horizontal Exits and the referenced 1026.5 Standpipes (Standpipes and standpipe hose connections shall be provided where required by Sections 905.3 and 905.4.)

Reply
Todd
4/8/2026 09:26:29 am

IBC-2024 905.4 Location of Class I Standpipe Hose Connections (SHC) includes the prescriptive requirements for a SHC at a HE :

905.4 Location of Class I Standpipe Hose Connections
Class I standpipe hose connections shall be provided in all of the following locations:
2. On each side of the wall adjacent to the exit opening of a horizontal exit.
Exception: Where floor areas adjacent to a horizontal exit are reachable from an interior exit stairway or exterior exit stairway hose connection by a 30-foot (9144 mm) hose stream from a nozzle attached to 100 feet (30 480 mm) of hose, a hose connection shall not be required at the horizontal exit.

Based on my calculations, the midpoint between the (2) IES is +/-147 FT so a HE located at this location would exceed the 130 FT maximum (30+100) exception as prescribed above.

Reply
Todd Wyatt
4/10/2026 07:45:35 am

CORRECTION : The halfway point between the (2) Interior Exit Stairways (IRS) is approximately 108 FT (not 147 FT) which WOULD meet the 130 FT maximum (100 FT of hose + 30 FT of hose stream) so additional standpipe connections at a central HE location would NOT be required.

Jack G
4/10/2026 08:10:10 am

Rather than put a standpipe hose valve in the middle of a corridor in the center of the building, and none are required at the building doors, a good point made was the firemen following the hose,
I would add 2, one inside each entry door, making it safer for the firemen to enter a burning building and the center corridor is protected from each side.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT