MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Standpipe Hose Connection Allowed in Corridor?

7/16/2025

8 Comments

 
Looking for clarification on NFPA 101 Section 30.2.5.1.2, which provides an exemption for exit staircase remoteness. NFPA 14, however, requires a standpipe system in all exit staircases.

We are working on an 18-floor high-rise apartment building that has two exit staircases eligible for the remoteness exemption outlined in 30.2.5.1.2.

I would like to install a standpipe riser in the exit access corridor leading to exit staircases instead of within the exit staircase, as NFPA 14 specifies.

Is locating the hose valves in the corridor in-between allowed rather than within the exit enclosure?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
7/16/2025 08:31:13 am

NFPA 14 Section 7.3.2.1 requires the connection to be provided at the stair landing for a Class I Standpipe System. Section 7.3.3.1 would cover the requirements for a Class II Standpipe System.

The connection is for the Fire Department and not for the building occupants.

The answer to your question is that for a Class I standpipe System is that it is not permissible to locate the connection in the exit corridor. It is permissible to locate a Class II Standpipe System connection in the exit corridor.

Reply
Todd E Wyatt
7/16/2025 08:54:54 am

The scoping Code (e.g. IBC-2024) references the standpipe standard (e.g. NFPA 14-2024 Standard for the Installation of Standpipe and Hose Systems) per 905.2 (see REFERENCES below). If the scoping Code has a more stringent requirement than the referenced Standard, the scoping Code governs.

IBC-2024 has different installation requirements for CLASS I, II, and III STANDPIPES.

905.4 Location of CLASS I STANDPIPE (CIS) Hose Connections requires CIS in every required Interior Exit Stairway (IES) whereas 905.5 Location of Class II Standpipe (CIIS) Hose Connections requires CIIS be located for "ready access."

Since this is a High-Rise Building (HRB), the standpipe location shall also meet Section 403 which requires standpipes located in IES that are remotely located per Section 1007.1.

Based on scaling the diagram, it appears the (2) IES are not separated by "not less than one-third of the length of the maximum overall diagonal dimension of the area served" as req'd by 1007.1 Exc #2.

Reply
Todd E Wyatt
7/16/2025 08:55:19 am

REFERENCES
IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 905 Standpipe Systems
905.2 Installation Standard
Standpipe systems shall be installed in accordance with this section and NFPA 14. Fire department connections for standpipe systems shall be in accordance with Section 912.
905.4 Location of CLASS I STANDPIPE Hose Connections
Class I standpipe hose connections shall be provided in all of the following locations:
In every required INTERIOR EXIT STAIRWAY OR EXTERIOR EXIT STAIRWAY, a hose connection shall be provided for EACH STORY above and below grade plane. Hose connections shall be located at the main floor landing unless otherwise approved by the fire code official.
        Exception: A SINGLE HOSE CONNECTION shall be permitted to be installed in the OPEN CORRIDOR OR OPEN BREEZEWAY between OPEN STAIRS that are not greater than 75 FEET (22 860 MM) APART.
905.4.1 Protection
Risers and laterals of Class I standpipe systems NOT LOCATED WITHIN AN INTERIOR EXIT STAIRWAY shall be protected by a degree of FIRE RESISTANCE EQUAL TO THAT REQUIRED FOR VERTICAL ENCLOSURES in the building in which they are located.
Exception: In buildings equipped throughout with an approved automatic sprinkler system, laterals that are not located within an interior exit stairway are not required to be enclosed within fire-resistance-rated construction.

905.5 Location of Class II Standpipe Hose Connections
CLASS II STANDPIPE hose connections located so that all portions of the building are within 30 feet (9144 mm) of a nozzle attached to 100 feet (30 480 mm) of hose. CLASS II STANDPIPE hose connections shall be located where they will have READY ACCESS.

Chapter 4 Special Detailed Requirements Based on Occupancy and Use
Section 403 High-Rise Buildings
403.3.1.3 Riser Location
STANDPIPES or sprinkler express risers shall be placed in INTERIOR EXIT STAIRWAYS and ramps that are REMOTELY LOCATED in accordance with Section 1007.1.

1007.1.1 Two Exits or Exit Access Doorways
Where two exits, exit access doorways, exit access stairways or ramps, or any combination thereof, are required from any portion of the exit access, they shall be placed a distance apart equal to not less than one-half of the length of the maximum overall diagonal dimension of the building or area to be served measured in a straight line between them. Interlocking or scissor stairways shall be counted as one exit stairway.
Exceptions:
Where interior exit stairways or ramps are interconnected by a 1-hour fire-resistance-rated corridor conforming to the requirements of Section 1020, the required exit separation shall be measured along the shortest direct line of travel within the corridor.
Where a building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2, the separation distance shall be not less than one-third of the length of the maximum overall diagonal dimension of the area served.

Reply
Todd E Wyatt
7/16/2025 08:55:50 am

REFERENCES

IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 905 Standpipe Systems
905.2 Installation Standard
Standpipe systems shall be installed in accordance with this section and NFPA 14. Fire department connections for standpipe systems shall be in accordance with Section 912.
905.4 Location of CLASS I STANDPIPE Hose Connections
Class I standpipe hose connections shall be provided in all of the following locations:
In every required INTERIOR EXIT STAIRWAY OR EXTERIOR EXIT STAIRWAY, a hose connection shall be provided for EACH STORY above and below grade plane. Hose connections shall be located at the main floor landing unless otherwise approved by the fire code official.
        Exception: A SINGLE HOSE CONNECTION shall be permitted to be installed in the OPEN CORRIDOR OR OPEN BREEZEWAY between OPEN STAIRS that are not greater than 75 FEET (22 860 MM) APART.
905.4.1 Protection
Risers and laterals of Class I standpipe systems NOT LOCATED WITHIN AN INTERIOR EXIT STAIRWAY shall be protected by a degree of FIRE RESISTANCE EQUAL TO THAT REQUIRED FOR VERTICAL ENCLOSURES in the building in which they are located.
Exception: In buildings equipped throughout with an approved automatic sprinkler system, laterals that are not located within an interior exit stairway are not required to be enclosed within fire-resistance-rated construction.

905.5 Location of Class II Standpipe Hose Connections
CLASS II STANDPIPE hose connections located so that all portions of the building are within 30 feet (9144 mm) of a nozzle attached to 100 feet (30 480 mm) of hose. CLASS II STANDPIPE hose connections shall be located where they will have READY ACCESS.

Chapter 4 Special Detailed Requirements Based on Occupancy and Use
Section 403 High-Rise Buildings
403.3.1.3 Riser Location
STANDPIPES or sprinkler express risers shall be placed in INTERIOR EXIT STAIRWAYS and ramps that are REMOTELY LOCATED in accordance with Section 1007.1.

1007.1.1 Two Exits or Exit Access Doorways
Where two exits, exit access doorways, exit access stairways or ramps, or any combination thereof, are required from any portion of the exit access, they shall be placed a distance apart equal to not less than one-half of the length of the maximum overall diagonal dimension of the building or area to be served measured in a straight line between them. Interlocking or scissor stairways shall be counted as one exit stairway.
Exceptions:
Where interior exit stairways or ramps are interconnected by a 1-hour fire-resistance-rated corridor conforming to the requirements of Section 1020, the required exit separation shall be measured along the shortest direct line of travel within the corridor.
Where a building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2, the separation distance shall be not less than one-third of the length of the maximum overall diagonal dimension of the area served.

Reply
Joe
7/16/2025 08:55:11 am

Reflect on the purpose it is serving....FIREFIGHTERS. Need to be hooking up to the hose outlet within the protection of the stairwell that it affords prior to entering the fire floor to attack the fire.

Reply
Dan Wilder
7/16/2025 09:06:54 am

NFPA 14 does allow a Class 1 standpipe hose connection to be located between stairs if they are in the open connecting corridor and travel distances are met (14-24' 9.5.2.1.2 and also in previous editions as I have used this for a layout). The diagram shown does not look to comply with this allowance so the locations would default back to each enclosed stair.

Reply
Chad
7/16/2025 10:46:19 am

It doesn’t matter what 14 says you need to do what the fire department wants in this case. They have the authority to tell you to move it….

Frankly, I don’t like having to leave the stairwell door cracked open to advance a hose line from there under fire conditions. Just my opinion.

Reply
Jesse
7/16/2025 01:16:02 pm

I can't see this as being a viable option. I'd run it by the AHJ, but I wouldn't expect them to agree to it

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT