For scissor stairs having 2 separate standpipe risers (one of them is a combined sprinkler and standpipe system) running 12 floors, how do we size the pump flow rate required?
Can we argue that we can use a 500GPM pump since the Risers are in close proximity to each other and are within one stairwell, or should we use a 750GPM pump following the NFPA 14 sizing of 500GPM plus 250 GPM per additional riser? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Anthony
11/19/2025 08:01:34 am
NFPA 14- 2024 ed
Reply
Anthony
11/19/2025 08:02:31 am
Reply
Glenn Berger
11/19/2025 08:24:15 am
One stairwell (stair enclosure) for a building with 12 floors???
Reply
Jack G
11/19/2025 10:16:03 am
They are to be considered as 2 standpipes so 500 for the first plus 250 gpm for the second And 250 for additional up ton1000 gpm applies.
Reply