Standpipe Connection On Floor Without Door?

11/6/2025

10 Comments

 
I have a hotel building that requires a standpipe in each of the two staircases. One of the stair shafts has a door to the outside at grade level, but there is no door to the first level inside. The lowest level with an interior door is the second floor, which has its own hose connection.

It doesn't make sense to provide a hose connection at the ground floor, but is there a code basis to support this?

Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder link
11/6/2025 06:57:41 am

Depending on your adopted and amended IFC...

905.4 has the required locations of hose connections.

As the stair does not access the inside of the building, then it's just confirmation that the horizontal exits that are on the first floor to comply with the 200' allowance per 905.4(6) as the responding apparatus becomes the "hose valve"....

Reply
Jesse
11/6/2025 08:25:52 am

I've seen this a time or two. And you're right; it doesn't make a lot of sense for a hose valve there. In all but one of the cases I've experiewnced, the AHJ didn't want a hose valve there. But then, in that one case, another AHJ did for some inexplicable reason.

My recommendation is to make your case to the AHJ as to wjhy the valve should be ommitted znd see what they say.

Reply
Anthony
11/6/2025 08:29:15 am

You have an intermediary landing. the stair access point (main landings) only exist where there is the option for entrance and egress. Thus, no I wouldn't think you'd need one where the code calls for a hose valve at the main landing as you don't have one.

Reply
Dwight H Havens
11/6/2025 08:43:07 am

I prefer to look at such a local requirement as providing resiliency for manual firefighting and maintenance . For example, it allows that standpipe to be shutdown and easily drained to the outside of the building while maintaining the rest of he standpipe system.

It also allows the FD to connect in and supply the standpipes from a different location when access to the building's FDC is a long way from where the closest access to a fire on an upper floor is from this stairwell, without requiring that a second engine be immediately available at the FDC location. Also, if there is an issue with the FDC, it provides an alternate means for pressurizing the standpipe.

Sometimes it is easier to take the hose valve on the floor below the fire floor when the fire is close to the stairwell on the second floor, rather than flaking the hose up and down the stairwell.

Reply
David
11/6/2025 10:33:06 am

Dwight, you are correct when stating they may use the 1st floor hose valve for a fire on the 2nd floor. Most (if not all) of the fire departments in the US train to connect to the hose valve on the floor below the fire. So, a fire on the second floor would use the 1st floor hose valve.
Your comments on using it as an alternate means to supply the system are spot on as well.

Reply
Andrew
11/15/2025 12:45:51 pm

I think the bottom hose connection as a redundant inlet is a good point to make and is well documented in FD training literature, however, for the other point, it should be understood that basically no fire department is going to be connecting to a standpipe for a second floor fire, or third floor. They will run their 200' preconnect whenever possible. They will add another 100' length to it before thinking about a standpipe.

Todd E Wyatt
11/6/2025 09:16:13 am

Yes, a standpipe is required in every Interior Exit Stairway (IES) at each story ... there is no exception for an IES that does not have direct access to the interior of the building at the level of Exit Discharge.

IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 905 Standpipe Systems
905.4 Location of Class I Standpipe Hose Connections
Class I standpipe hose connections shall be provided in all of the following locations:
1. In every required interior exit stairway or exterior exit stairway, a hose connection shall be provided for each story above and below grade plane. Hose connections shall be located at the main floor landing unless otherwise approved by the fire code official.

Reply
Glenn Berger
11/6/2025 09:31:52 am

I suspect that the first level has a dedicated exit to the exterior at this location. I would then locate the hose valve near this exit.

Reply
Matthew Mueller
11/7/2025 06:52:21 am

While I am not familiar with a code that may or may not require this, I do know that some fire department SOPs call for the attack line to be connected one story below the fire floor. If this is the case it would make sense.

Reply
Jack G
11/11/2025 01:58:23 pm

Years ago in the 90 s ,hose connections for the ground floor were optional as the fire trucks had access. When the hook ups changed to one floor below, they were again required.
One in the egress is required. In a situation like the
Is I put one in the lobby next to the stair on the ground floor as a fail safe if the 200 feet separation is exceeded.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT