Is this an allowed and feasible installation for FHV's that are required to be installed at intermediate landings, to avoid penetrations in a precast stair?
Is there a code basis against this, or any differing recommendations on routing here? See image below. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Glenn Berger
4/22/2026 08:14:21 am
The height of the hose connection and valve may be an issue.
Reply
Todd E Wyatt
4/22/2026 08:16:33 am
See "Standpipes: Floor vs. Intermediate-Level Landings" (https://www.meyerfire.com/blog/standpipes-floor-vs-intermediate-level-landings)
Reply
Dan Wilder
4/22/2026 08:19:33 am
Allowed, sure in theory.....however I wouldn't recommend it. Although I have seen it before with the hose valve/standpipe 180° rotated from this illustration.
Reply
4/22/2026 10:57:22 am
Guardrails are required to be 42" above the finish floor level. (IBC & NFPA 101)
Reply
Ricardo Gonzales
4/22/2026 08:27:09 am
Before installing this work, I like the idea, coordinate with structural and the AHJ to make sure each platform can handle the weight at this location.
Reply
Jack G
4/22/2026 08:28:42 am
Yes, as long as they adhere to the protection standards of NFPA 14.
Reply
Jack G
4/22/2026 09:02:46 am
Vic’s——if EQ zone, will need them each side of the landing .
Reply
Jesse
4/22/2026 08:39:17 am
The only issue I can see is height of the hose valve as it relates to the handrail.
Reply
Anthony
4/22/2026 09:52:26 am
I like this arrangement for non compliant landings. Where no matter where you put the standpipe you'll be in an egress path. Also only in retrofits. I don't like this for new builds at all, work with the architect and design team to make the stair larger enough to accommodate the FP in new builds in main landings.
Reply
Jose R Figueroa
4/22/2026 10:04:19 am
To the best of my knowledge, no standard prohibits this arrangement, and it is not that uncommon. Please ensure that you consult with the FD/AHJ before commencing the project. The issue may stem from the lack of access to the valves and outlets required for the FD.
Reply
Brevin Holden
4/22/2026 10:40:00 am
I think everyone above is correct and has great comments. Also, assuming this is a rated stairwell enclosure, I would be interested to see how they sleeve around the piping in through penetrations like the floor levels.
Reply
Max B - AFPC Corp
4/22/2026 11:41:12 am
Thinking about hanging requirements I remembered that victaulic has No.A191 carbon steel anchor outlet fitting.
Reply
Ryan Grant
4/23/2026 08:54:28 am
From an AHJ/firefighting perspective, I find it problematic. It will obstruct the stairs and hinder movement.
Reply
Larry Kaufman
4/24/2026 08:07:24 am
From an operations standpoint this arrangement would be problematic.