Is sprinkler protection necessarily required beneath translucent, sloping roof structures located above large vertical openings extending through multiple levels of an open parking structure, where the roof perimeters remain open to the surrounding atmosphere?
This project is under NFPA 13 (2022) and NFPA 88A (2023). If sprinkler protection is required, are there technically acceptable alternative arrangements to a conventional sprinkler grid beneath each roof, and what specific provisions govern their design and approval? I would appreciate references to the applicable code sections and any relevant engineering experience. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
11/4/2026 06:40:11 am
Assuming the parking structure is large enough to require sprinklers, yes, the translucent sloped ceiling over the large open vertical shaft still can collect heat and still requires protection.
Reply
Chad
11/4/2026 08:04:36 am
Pete is right as if it can collect heat it should be sprinklered. That's basic NFPA 13.
Reply
Jeff M Ayers
11/4/2026 02:16:08 pm
Chad,
Reply
Jesse
11/4/2026 08:10:32 am
Yep, it still needs to be protected. Tjhe translucent ceiling will still collect heat.
Reply
Elena V.
11/5/2026 11:46:49 am
I don't think it is this the problem, au contraire, this endorse my objection to install sprinklers there. They need to operate after 108 oC, since Greek summer is a boiling pan. Furthermore, this concerns an open parking area with a floor area exceeding 10,000 m². If a fire were to occur on the ground floor—23 meters below the canopy (which is not a skylight, I repeat)—the the probability that the 108°C-rated sprinklers are triggered implies that the fire has become widespread throughout the building; consequently, many other sprinklers would have already activated before the temperature reached this high level. For this reason, I maintain that the area of the footprint directly beneath the opening must be protected at the ground-floor level, rather than at the level of the canopy situated above the roof of the top floor.
Reply
Elena V.
11/4/2026 08:32:15 am
he vertical openings are through a 7 storey building and over the roof slab, at 1,5m height over the slab, with all the perimeter open over the roof, there is just a canopy. What is the use of the sprinklers over a void of 23 m. The air drafts won't let the water reach the floor
Reply
Chad
11/4/2026 03:09:56 pm
Elena-
Reply
11/4/2026 08:33:49 am
Well, let's think about this. You describe what is essentially a rain shield over an open shaft. You state that this sloping cover is open on it's perimeter so smoke and heat will flow out. They may be able to slow the flow enough to operate sprinklers, but what are you expecting the water to fall upon in this open shaft? Is there a fire load or fuel beneath? What is the hazard that we are trying to extinguish?
Reply
Elena V.
11/5/2026 11:36:51 am
That's right. I have a continuous conflict with the other FLS. He can't justify the use of sprinklers at that height, but he insists.There are cars on the ground floor on the bottom of this vertical opening and I proposed a combination of beam fire detection and a small deluge (2 x 4 side sprinklers, extended coverage placed on the beams in the two opposite sides). He is stuck on the sprinklers under the canopy. I told him we are going to need a catwalk, but no response.
Reply
Glenn Berger
11/4/2026 09:43:38 am
Depending on the version of NFPA 88A is applicable, sprinklers may be required. Probably need to work withe structural enginner to provide hanging points for t he sprinkler system.
Reply
Todd E Wyatt
11/4/2026 10:22:28 am
The scoping Code (e.g. IBC-2024) determines WHERE an automatic sprinkler system (ASPS) is required. For PARKING GARAGES (PG), 903.2.10 bases it on the fire area of an enclosed PG (>12000-SF) or on the fire area of an open PG (>48000-SF). If your PG meets these prescribed requirements, the PG shall be protected by an ASPS “throughout.” Only the referenced ASPS Standard (e.g. NFPA 13) can then determine where in the PG the ASPS can be omitted.
Reply
Streeter
11/4/2026 04:19:17 pm
Man this question would benefit greatly from pictures. The default answer is yes, treat sprinkler requirements here like any other canopy or overhang. The only true way out would be getting an FPE to assess the true effectiveness a system would have here and work with the AHJ to allow an engineered solution if possible.
Reply
Jack G
11/5/2026 01:12:21 pm
My opinion, no brainer. If it traps heat or deflects flames, then protect it.
Reply