Are sprinklers required in a noncombustible concealed space that contains combustible insulation?
I have a contractor who is trying to use polyurethane spray foam insulation in a noncombustible concealed space above a ceiling. It is an NFPA 13 system and they do not want to sprinkler it. To my knowledge, this spray foam insulation is combustible, and by filling a noncombustible space with it, it will need sprinklers. They are trying to propose intumescent paint, but I don't believe that changes anything for them. Do you all know of any applicable exceptions in this situation or if they don't need sprinklers? I think 9.2.1.13 is the only relevant section from 13, but I am having trouble finding whether this foam exceeds the 1,000BTU per square foot. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Jesse
8/11/2026 08:30:09 am
In order to omit AS protection in the atic, the void needs to be filled with non-combustible or limited combustible insulation. There are many spray foam insulation products that are cocmbustible, and that would negate the reasoning for omitting protection there.
Reply
anthony
8/11/2026 09:02:57 am
Jesse has it here. Add combustible construction to an otherwise non combustible space it becomes a combustible space. This isn't a trick question here.
Reply
OP
8/11/2026 10:54:20 am
This was my thinking. Just wanted to make sure I wasn't being ignorant because the customer does not agree with me and I like to check myself before putting my foot down.
Todd Wyatt
8/11/2026 08:34:11 am
The scoping Code (e.g. IBC-2024) requires WHERE an automatic sprinkler system (ASPS) is required to be installed per Occupancy Classifications, Specific Building Areas and Hazards, and/or during Construction.
Reply
Todd Wyatt
8/11/2026 08:34:55 am
REFERENCES
Reply
Erik
8/11/2026 09:07:43 am
9.2.1.1 NFPA 13 (2019) - Concealed spaces of noncombustible and limited combustible construction with MINIMAL combustible loading having no access shall not require sprinkler protection.
Reply
OP
8/11/2026 10:56:34 am
Thank you for clarifying. I also believe this is above the threshold of minimal combustible loading but I also understand that is an engineering judgement and was looking for second opinions.
Reply
Jack G
8/11/2026 09:41:35 am
Erik has it correct.
Reply
zackery geddies
8/11/2026 01:22:09 pm
take a look at Mineral wool such as Rock wool. It is non combustible and it has a thermal value.
Reply