I have a F-1 occupancy used for powder coating lines for RV chassis, fully-sprinklered except for the equipment (booths). Inside of this facility there are large powder coating, ovens and media blasting booths that the chassis run through on a track. Each booth is about 18’ x 30’.
Would the media blasting booths require fire protection? The customer does not want to install FP for the media blasting in fear of an accidental discharge that would stop most RV production for the entire country. My thought is the blasting booths along with the powder coating would require FP due to size and I cannot find any exceptions except for the ovens per IFC, class A&B ovens not used for combustible products. Any thoughts? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Jeremy James
5/11/2021 08:25:44 am
I would think that these need to be protected also. What does the customers insurance company suggest? I'd recommend starting there. Also, if the customer is worried about accidental discharge, provide the option of a single or double interlock pre-action.
Reply
Joshua Freedman
5/11/2021 10:15:01 am
NFPA 30 (2018) states in chapt 15:
Reply
Franck
5/11/2021 01:46:42 pm
It’s a definitive YES.
Reply
Scott
5/12/2021 04:40:04 pm
We know the powder coating booth definitely require FP, the unknown is the media blasting booths which are quite large. I believe they would require it under IFC 902.3 ( I believe, don’t have the book with me) that references obstructions over 4’ including equipment.
Reply
DavdiC
5/11/2021 06:28:46 pm
Also consult with the AHJ as they may have different requirements. We would not allow a Dry Chem system in a booth that is within a sprinklered building. (I say not but we have had (1) exception to that).
Reply
Scott
5/12/2021 04:42:15 pm
David,
Reply
Franck
5/17/2021 04:02:56 am
As indicated above, some of the guidance I use for powder coating:
Reply
Ryan
6/17/2025 02:08:49 pm
Hi Jim, Im also just doing one of these powder coating lines. What did you end up doing here out of curiosity