Sprinklers Required for Large, Accessible Chase?

4/9/2026

16 Comments

 
In a four-story educational building, we have a large pipe chase that wraps around the men’s and women’s restrooms on each floor. The highlighted area in the attached sketch is the pipe chase area.
Picture
​The wall on the left (with the red arrows pointing at it) is a 1 hour rated shaft wall. All the other walls around the pipe chase are non-rated wall assemblies. There are doors (blue boxes) giving access to this area in three different locations. There isn’t any equipment or sources of ignition located inside the chase, just plumbing pipe.

While the area is not to be used for storage, we are concerned that the presence of the doors will allow people to do so. The Architect/Engineer has directed us not to protect this area with sprinklers.

Are sprinklers required inside this chase or can they be omitted as directed by the A/E?

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Peter Howard
4/9/2026 06:11:04 am

There's a door. It will inevitably get used for storage, official designation or not.

If you can get the client to agree to post "FOR MAINTENANCE PURPOSES ONLY - NOT FOR OCCUPANCY OR STORAGE" at that door, you might get the AHJ to agree that it won't be and go with the architect/engineer's plan to omit protection.

But without that signage, I see the AHJ requiring protection due to accessibility.

Reply
Dan Wilder
4/9/2026 07:42:41 am

Yep...not just a single door, 3 doors and a lot of wall space available. I don't see an AHJ letting this one go. Maybe if those were only access panels it would be a better argument for omission.

Reply
Paul Pinigis link
4/9/2026 08:11:37 am

Why on earth do they need doors into this chase in the first place? Why not simply have the architect. Change these from doors to hatches and eliminate the whole concern.

Reply
KARLIN ROBERT JON
4/11/2026 12:56:32 am

this! raising the threshold of the door. eliminating a doorknobs. as well as limiting its size will help you win this argument that the access is prevents occupied use or storage - there are exemptions for pipe chases.

Reply
Glenn Berger
4/9/2026 08:11:54 am

What a waste of floor space. Sprinkler protection will be required.

Water closets and urinals require space behind them for their supports and "larger" waste and vent piping. Sinks do not require chase space behind them.

Reply
Kevin
4/9/2026 12:48:55 pm

Hi Glenn,

I read this every morning to develop my knowledge. That said, I don't understand what you mean by, "Water closets and urinals require space behind them for their supports and "larger" waste and vent piping. Sinks do not require chase space behind them."

But I would like to learn what you mean. I'm probably missing the obvious but appreciate you teaching me what you are referring to.

Take care and thank you - Kevin

Reply
Brett
4/9/2026 01:21:57 pm

Hi Kevin,

I am not Glenn (obviously) but if you search for pictures of water closet carriers then you'll see what he means. These are used for wall hung water closets.

Glenn
4/9/2026 03:32:44 pm

Kevin is spot on - The wall hung units have a sizeable support carrier associated with them. Waste piping is a minimum of 3 inches and sloped.

Arthur Gould
4/9/2026 08:38:01 am

I agree with Glenn that sprinkler protection will be required.

Reply
Gary Sims
4/9/2026 09:02:26 am

Is this project being designed to meet NFPA 13 criteria? If so, that is for a "fully sprinklered" building... not a partially sprinklered building. They are calling it a 'chase', so why does it have doors? "for maintenance"... so then it's a maintenance space. They're trying to use naming convention in an attempt to avoid fire protection. I suggest you request the A/E obtain a formal variance/ authorization from the AHJ to omit fire protection. Make them do the work and provide copy to you. It protects them, you, and the owner. They are putting you in a bad position where you can't win. You could also size your pipe accordingly (to supply that area) and hit 'em with a nice change order when the AHJ makes you add fire protection.

Reply
Jack G
4/9/2026 09:41:12 am

Access panels will let them slip by but doors not.
The more important thing is wraps, paper towels, cardboard accumulating “ by the maitanance “ man/ plumber. And of course smoking and a smoldering cigarette or cigar—— fire.
So better protect the space.

Reply
Jose R Figueroa
4/9/2026 10:41:19 am

A.S. are not necessary. If those areas are ever used for storage, the principal should be reprimanded and a Housekeeping policy should be put in place. I have seen storage of cables, cardboard boxes, and old PCs in electrical rooms. That would not justify installing sprinklers. Without a proper Housekeeping policy, sprinklers may become ineffective, such as storing idle pallets in the aisles of rack storage.

Reply
Wes
4/9/2026 10:55:26 am

What's the code basis for this?

If the space is considered accessible, which in my opinion this would be since there are three doors, there would be no provision in NFPA 13 to allow omission of sprinklers.

The allowance to omit sprinklers in noncombustible and limited-combustible spaces are for "concealed" spaces, not for accessible spaces like this, per Section 9.2.1 (2025 Edition).

I'm with the other responders about a small access panel could still qualify as a concealed space, under NFPA 13.

Reply
Justin
4/9/2026 04:13:33 pm

I agree with the other comments that in this current configuration, sprinklers are required in the space. However, the primary contributing factor is the doors accessing the space. If the doors could be replaced with hatches (or similar), I would classify this space as "Normally Unoccupied Building Service Equipment Support Area" per NFPA 101 and then see reason to qualify as a concealed space per NFPA 13 to omit sprinklers.

Reply
Jon N
4/9/2026 07:04:08 pm

In my former life as an AHJ, I supervised a state public school fire inspection program. Schools never have enough storage, and I can almost guarantee that eventually this space will be used for storage (especially convenient for paper products). Signage doesn't typically work well in schools or at least it isn't followed. Doors make it a room and storage is highly probable. Sprinklers should be installed.

Reply
Donnie
4/9/2026 07:34:08 pm

No doubt sprinkler protection would be required in accordance with NFPA 13 for the accessible space.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT