Sprinklers Required Below Mesh Green Ceiling?

1/10/2025

10 Comments

 
I am working on a sprinkler system where the corridor has a wooden ceiling, as shown below. Upright sprinklers protect the space above the ceiling.

I want to know whether the pendent sprinklers below the ceiling are also required?

Is this an open grid ceiling under NFPA 13?

The ceiling has the following characteristics: Bamboo ceiling panels with mesh void and solid wood frame with galvanized black metal rods as hangers for proper support, panels are to have a consistent panel size of 15 cm void between each panel and the wall and 30 cm void between the panels for the greenery to be hung.

Can anyone help me in this case? Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
10 Comments
Pete H
1/10/2025 06:44:17 am

From NFPA 13 (2016 Ed.)

8.15.14 Open Grid Ceilings. Open Grid ceilings shall only be installed beneath ceilings where one of the following is met:
1) Open grid ceilings in which the openings are 1/4 in. or larger in the least dimension, where the thickness or depth of the material does not exceed the least dimension of the opening, and where such openings constitute 70% of the area of ceiling material. The spacing of sprinklers over open grid ceilings shall comply with the following:
a) in light hazard occupancies where sprinkler spacing (either spray or old style sprinklers) is less than 10 ft x 10 ft, a minimum clearance of at least 18 in. shall be provided between the sprinkler deflectors and the upper surface of the open grid ceiling. Where spacing is greater than 10 x 10 ft but less than 10 x 12, a clearance of at least 24 in. shall be provided, and at least 36 in. for old style sprinklers. Where spacing is greater than 10 x 12, a clearance of at least 48 in. shall be provided.
b) In ordinary hazard occupancies, open grid ceilings shall be permitted to be installed beneath spray sprinklers only. Where sprinkler spacing is less than 10 x 10, a minimum clearance of at least 24 in. shall be provided. Where spacing is greater than 10 x 10, a clearance of 36 in. shall be provided.
2) Other types of open grid ceilings shall be permitted to be installed beneath sprinklers where they are listed for such service and are installed in accordance with instructions contained in each package of ceiling material.

A.8.15.14 The installation of open grid egg crate, louver, or honeycomb ceilings beneath sprinklers restricts the sideways travel of the sprinkler discharge and can change the character of discharge.

-----

Okay, so I'm leaning towards this isn't an open grid.

It doesn't look a full 70% or greater open, it looks like it's thicker than the opening between the grid lines. But that is me evaluating based on a picture and not actual details or technical specs of the ceiling.

I'd protect underneath it, ideally with a line of corridor sidewall sprinklers.

Reply
Dan Wilder
1/10/2025 07:52:50 am

Even without the additional lower ceiling, there should be obstruction protection within this corridor due to the mostly solid cable trays and additional duct work. The added ceiling just allows the protection to be a little lower overall.

I would be dropping sprinklers to cover beneath the bamboo via a drop/arm-over/upright-pendent or a drop with a pendent and a water shield within 3" of the perimeter on the sides that do not have the additional hung greenery.

Reply
Glenn Berger
1/10/2025 08:15:58 am

Pete cited the code definition for open grid ceilings and like Dan stated, the photo does not support the open grid concept. I am in agreement with both respondents.

Reply
Chris
1/10/2025 08:33:46 am

Is this an interior finish in an egress corridor? I'd recommend looking into this as well.

Reply
Jimmy
1/10/2025 08:47:08 am

Bingo!
This should have never been approved,
BUT something tells me it was never permitted.

Hopefully it will be inspected and addressed by a qualified official.
Soon,

Reply
Jose R Figueroa
1/10/2025 12:30:50 pm

Sprinklers should be installed inside concealed spaces and beneath suspended combustible ceilings. According to my interpretation of NFPA 13, any area above a grid ceiling that does not meet the "open grid" criteria should be considered a concealed space. Therefore, sprinklers may need to be installed above it unless the construction materials and potential fire load in that space meet specific conditions that allow for an exception, as outlined in section 9.2.1 regarding allowable unsprinklered concealed spaces in the standard.

If I may add, this area originally resembled a hospital basement corridor. I find the new construction design intriguing. Why is there greenery on the false ceiling? Is it related to some environmental regulations? I might have misunderstood the description. What are the local code requirements? AHJ? Thank you

Reply
J.H.
1/10/2025 03:06:35 pm

Great feedback from all. A few years ago we had a project come through with proposed nylon mesh providing shade to an outdoor garden center, attached to the main, sprinklered structure. They came into Code compliance by providing sidewall sprinklers of sufficient coverage.

In addition to following up on the interior finishes, I would make the recommendation that the edges of the steps in the gray concrete corridor be marked in a contrasting color. One of our inspectors fell down some virtually invisible gray concrete steps, similar to that one, while walking an overhead visual inspection. They survived, but needed years of PT.

Reply
Jack G
1/10/2025 03:11:42 pm

Whether the ceiling is 70% open or not there is not enough room for the sprinklers above the mesh, so sprinkler protection must be added below. From the pictures I cannot see any visible existing sprinklers that were protecting the corridor.

Reply
James E Art Fire Protection Engineer (FPE)
1/13/2025 04:57:31 pm

Just wondering
Q. What are those things that look like ducts with
lots of holes?
Maybe cable trays?

Clear example of Architects or Others more concerned with appearance than function!

I'm working with a winery client in the boondocks,
who is concerned with the slope of the roofs on a series of corrugated steel fire water tanks.

Reply
Donald Pierce link
1/15/2025 12:06:23 pm

One more comment: This ceiling is not static. The living, growing plants not only have the potential to obstruct horizontally but vertically. Sprinklers above and below and be mindful of small hanging obstructions that could become significant.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT