Sprinklers Req'd Over Kitchen, Laundry in 13/13R?

3/3/2026

7 Comments

 
We have a 4-story motel that the architect of record stipulated the sprinkler system was to be designed in accordance with NFPA 13R. The building is wood construction with open wood joists. We have a kitchen and several laundry rooms that have suspended ceilings, which would be designed in accordance with NFPA 13 Ordinary Hazard Group I Occupancy.

What about the combustible area above the ceiling in the combustible area above the suspended ceiling in the laundry room?

​Are sprinklers required in this space?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/3/2026 06:27:54 am

The building is still 13R. The combustible ceiling above the kitchen is the same as a combustible ceiling in 13R. The use of NFPA 13 to design the common kitchen and other spaces does not apply to interstitial spaces outside of the kitchen or other accessible common rooms unless required by 13R.

Reply
Brett
3/3/2026 06:48:55 am

Is the entire building 13R?

If the whole building is 13R, just follow 13R's rules for putting sprinklers in ordinary hazard spaces. The combustible concealed spaces don't need to be covered unless you fall into one of the scenarios from IBC section 903.3.1.2.3 where sprinklers are required (example - the attic is used for storage).

Sometimes buildings are setup with NFPA 13R and NFPA 13 areas in the same building.

In low-rise residential buildings, sometimes non-residential occupancies are separated with fire barriers and floor/ceiling assemblies with those portions of the building being sprinklered per NFPA 13. Typically this is only done when those occupancies occupy more than 10% of the floor area and don't qualify as being accessory to the residential occupancy.

Laundry rooms are typically an incidental occupancy which is different than an accessory occupancy.

If you have this setup then you need to know where those fire rated assemblies are and then you can figure out how to deal with the combustible concealed spaces.

Reply
henry henchal
3/3/2026 08:08:04 am

Per the IBC the floor / ceiling assemblies will require a rating (drywall) so just suspended ceiling is probably not correct - unless they have the drywall on the bottom chords and the ACT below?

Reply
Glenn Berger
3/3/2026 08:43:12 am

Need to validate that the NFPA 13R is the correct standard to be used. (Not enough information is contained in the comments to confirm.)

From experience, the height of the facility has caused me issues in the past as it exceeded the limits of NFPA 13R.

Reply
Bobby
3/3/2026 09:42:41 am

Start with local building codes and ordinances to verify if the applicable standard is NFPA 13R.

2019 NFPA 13R, section 6.2.2.2(6), allows use of residential sprinklers in this area. This section also directs you to section 7.2.4.1. Under that section, the only mention of NFPA 13 design refers to “discharge densities.” Thus, I would say that no, sprinklers are not required above ceiling in this space. However, look at section 7.4 for requirements for fuel-fired equipment or if the space is used for storage.

Reply
Jack G
3/3/2026 09:43:02 am

As long as the building can be classified as 13 r. There are restrictions ( see MeyerFire 13-13r-13-d cheat sheet ) thing like area and or height increases, whether it has VA constriction etc. it then has to be an NFPA 13 system.

Reply
Dave L.
3/3/2026 10:47:58 am

Most architects I deal with are capable of determining the correct code path, but occasionally I have to remind them that 13R is Life Safety Only (thus does not provide 100% coverage), as Matt Klaus explains in this NFSA video. This video is several years old, but still applicable.
https://youtu.be/fQWLxjWsD68?si=mjczlN8T_BheJkhp

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT