Canopies and overhangs have been discussed extensively, including the Meyerfire article and Exterior Projection Cheatsheet.
I know when and how NFPA 13 requires protection, but I am finding architects often provide a "gap" between the face of the building and an exterior canopy. Sometimes this gap is very small. I have had an AHJ tell me a gap of any size results in no protection required, even if a roof overhang overlaps above. I'd like to ask the building code experts here if this is a function of if the area beneath is considered part of the Fire Area. Once again I have a project where it is a wide canopy of combustible construction, would require protection beneath, but it is free-standing, with just a couple inches gap between the canopy and the exterior wall of the building. Sprinklers required, or not? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/17/2022 07:00:10 am
If the AHJ told you they're not required... then in their jurisdiction, they are not required.
Reply
Alex
6/17/2022 07:28:24 am
Pete is right above, if the AHJ is saying no protection, there is your answer.
Reply
Jesse
6/17/2022 08:04:51 am
I agree with Alex and Pete. It really is the AHJ that makes the final interpretation.
Reply
Todd E Wyatt
6/17/2022 08:31:50 am
Are Fire Sprinklers Required for a Canopy?
Reply
Glenn Berger
6/17/2022 08:35:32 am
Make sure that you have the signed documentation from the AHJ in your files. AHJs do change and their interpretation of the code can vary.
Reply
Greg
6/17/2022 08:37:20 am
If we accept the AHJ interpretation of what not to protect, does that decision inform us differently on the protection we know to have.
Reply
Wes
6/17/2022 08:42:00 am
Fundamentally, does it make a difference if there is a 2" gap between a Porte Cochere and the building, or none?
Reply
Chris
6/17/2022 08:47:56 am
I love Pete's comment "Grey areas are fun". This is the best way to interpret code as a whole.
Reply
Franck
6/17/2022 09:34:41 am
Everything has been said above.
Reply
Dwight H Havens
6/23/2022 09:18:21 am
Wow! Lots of good general approach information, but very little discussion on what the code requires (it depends upon many factors not provided here), and a lot of dumping the decision on the AHJ. You need to know and understand the code requirements before you initiate a discussion with the AHJ. Minimum sprinkler protection requirements generally originate in the building and fire code, but insurance companies may implement additional requirements based on specific needs.
Reply