To what extent are sprinklers required for an above-ceiling mechanical platform in noncombustible construction?
See the building section attached. In this case, the platform is nearly the full length of a classroom building.
17 Comments
Anthony
7/31/2024 07:35:11 am
Sprinklers are definitely required. Is there a way for a human to access the area? If yes, then its occupiable and thus requires sprinkler protection.
Reply
Glenn Berger
7/31/2024 08:07:26 am
The fact that a platform is provided would require the installation of sprinklers in the ENTIRE space, if the facility is desired or required to be fully sprinklered.
Reply
Todd E Wyatt
7/31/2024 08:10:07 am
Yes, an Automatic Sprinkler System (ASPS) is required here.
Reply
Dan Wilder
7/31/2024 08:18:48 am
You may be able to utilize a hybrid version of 9.3.14 for sprinkler locations/limitations but that would extend a minimum of 24'. There is definitely a sprinkler requirement due to access, ability to store, and the mechanical equipment.
Reply
James Phifer
7/31/2024 08:52:48 am
This is a non-combustible concealed space. Unless the platform is constructed of wood or other combustible materials or if there is fuel fired equipment, sprinklers should not be required.
Reply
Jesse
7/31/2024 09:49:31 am
I can't see a circumstance where protection can be omitted. You're going to have mechanical equipment which is electrical in nature (and maybe combustion fuel trains?) and personnel have the ability to access it.
Reply
Jack G
7/31/2024 10:17:46 am
On a mechanical equipment platform there usually is a trail of combustibles left behind by service men plus storage in the way of filters, foam insulation coated wire and more( why would they store that stuff anywhere else).
Reply
Lawrence
7/31/2024 11:11:27 am
Wow! Same condition right now on job and sprink guy asking same question! Following another response I go for defaulting to requiring the sprinklers and asking AHJ for opinion in writing.
Reply
Jack G
7/31/2024 11:53:48 am
Spot on. Good luck Lawrence !
Reply
Chad
7/31/2024 02:03:04 pm
Serious question:
Reply
Lawrence Stephens
7/31/2024 03:41:51 pm
that's the other half of my thinking also - fact is it must be occupied intermittently as HVAC gear requires regular maintenance, arguable and quite serious - where does the Christmas decorations, paper products, signage end up - you guessed it. Put in the sprinklers and you're not looking over your shoulder.
Reply
Anthony
8/5/2024 09:58:35 am
NFPA 13 makes the distinction between mechanical equipment that has ports for human access and its housing environment.
Reply
Robert W Hughes
7/31/2024 03:50:37 pm
James Phifer's interpretation seems correct to me, given the limited details. It is up to the owner to keep stored goods elsewhere, and they ALWAYS want to save money.
Reply
RC
7/31/2024 04:29:23 pm
I agree, sprinkler the area. But to what extent? The platform area is open to the entire above ceiling space. Figure A.9.3.14.3 does not really reflect this condition.
Reply
Mark Harris
8/5/2024 04:33:07 pm
Great discussions and my gut reaction based on construction agree with James about no- combustible space. But see the other arguments. Is there a stair that makes it a floor or does HVAC tech have to get to that unit through an acess panel through the main floor ceiling? I don't know where project is but if you do end up protecting confirm that attic will be over 40 degrees or you need to look at a dry system. If the only reason for sprinklers is the platform that could be an expensive platform when you add the cost of sprinklers in.
Reply
4/18/2025 07:14:14 am
This provides a great opportunity to work with the community and AHJ on the project. We are currently working on a school with a very similar layout in Texas and through discussions with the AHJ we have agreed on providing coverage to the mezzanine platform only as it was decided that this met the intent of the standard.
Reply