When is a cloud ceiling a ceiling, and when is it an obstruction?
I have a project with a 2-story lobby that has a mezzanine waiting area and clouded ceilings. The clouds are 3'-10" wide continuous clouds that run east/west across the room. The rows of clouds are spaced 4'-0" apart from each other but will have lights and diffusers between them serving the space. Spacing between the clouds and the wall varies but narrowest dimension is 2'-0". Even better, the roof above the cloud ceiling is sloped greater than 2/12" and will require an increased design area and sprinklers at the peak. The architect's intent was to not require sprinkler coverage below the ceiling clouds and consider them an obstruction not wider than 4'-0". I am not as comfortable with this but wanted to bring it up for discussion. I did see a forum post about this come up in 2022 but was wondering if anyone had additional comments. Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
10/28/2024 08:04:23 am
Do you happen to know the difference in elevation between the deflectors at the top and the 3'-10" wide ceiling clouds? Also what type of heads are being used?
Reply
Glenn Berger
10/28/2024 08:36:07 am
What is the difference in elevation between the cloud ceiling / obstruction and the ceiling deck above?
Reply
Dan Wilder
10/28/2024 08:41:36 am
Yes....and no...
Reply
Chris Nelson
10/28/2024 09:23:45 am
Architects and their pursuit of aesthetic is the antithesis of FPEs and their pursuit of safety
Reply
Jack G
10/28/2024 09:30:10 am
Agree with above. The clouds should have sprinklers in them or dropped thru the open spaces and armed to 6 inches beneath them in a spacing pattern to cover the floor.