We have a church with a raised platform (wood construction) that is not accessible and is a concealed space. We typically have not provided sprinklers for this type of space. The AHJ is stating sprinklers are required per NFPA 13.
Are sprinklers required for a combustible, concealed space below a raised platform? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
10/28/2025 07:25:03 am
Check NFPA 13 to whatever your AHJ's current accepted edition is.
Reply
Donnie
10/28/2025 07:59:15 pm
Clearly all 4 conditions exist that would allow you to omit sprinkler protection from the concealed space underneath the platform.
Reply
Chad
10/28/2025 08:11:51 am
Just fill it with non-combustible insulation? That would be a better alternative for an existing condition than sprinklering a blind space under a stage that will never get inspected, ever. IMO.
Reply
Anthony
10/29/2025 08:22:10 am
I was thinking about this a bit yesterday. what if there is a floor/basement beneath the platform doe this then qualify as a ceiling combustible space?
Reply
Wes
10/29/2025 08:39:36 am
I was curious to begin with (but hadn't weighed in yet) why it wouldn't qualify as a combustible concealed space to begin with, even without a floor below?
Reply
Anthony
10/31/2025 08:01:53 am
@wes
Jack G
10/29/2025 04:39:50 pm
I m assuming that you are talking about a raised combustible wood “ altar “ that is walked upon by church priests/ ministers.