Sprinkler Type for Tires with Limited Clearance?

8/20/2024

6 Comments

 
We have a project that is a retail tire store. In the back, there is a Tire Storage Room with a mezzanine of open grate flooring that takes up the majority of the floor plan for the room. The top of the open grate flooring is roughly 10-ft and the top of the roof decking is about 11-ft above the mezzanine.

Tires are stored on racks on both levels.

I think that CMDA sprinklers are the only real solution here because of the clearance to storage requirements. But, if we tried to use CMDA or ESFR, the owner would have little usable storage height.

Can anyone think of another good solution?

We have FP plans as part of the bid documents, and they specified something that won't work, so we kicked back an RFI for clarity, but we thought it would make good discussion here.
6 Comments
Peter Howard
8/20/2024 06:49:35 am

If you're worried about storage height, I would say CMDA is your best shot as long as it's single row racks and you have the water to go extra hazard group 1 as per table 13.2.1 (NFPA 13 2016 edition).

Reply
Todd E Wyatt
8/20/2024 08:35:14 am

From NFPA 13-2019's "Enhanced Content" for 23.8 ESFR Protection of Rack Storage of Rubber Tires :

The criteria for rubber tire storage being protected with ESFR sprinklers can be found in Table 23.8. Note that the table contains protection for a wide range of storage arrangements, including laced tire storage, which is the most difficult tire arrangement to protect. In a laced tire array, one tire is set at an angle into the hole of a tire below it. Another tire is then inserted at a right angle to that one with its tread in the hole of the tire below it (see exhibit below). Because the tire above blocks sprinkler discharge to the tire below, the laced array is extremely challenging to protect. ESFR sprinklers can protect laced arrays, but the discharge must be increased from the typical 12 sprinklers to 20 sprinklers (five sprinklers on four branch lines) with a minimum design area of 1600 ft2 (149 m2). Unlike other commodities protected with ESFR sprinklers, a rubber tire storage fire is only controlled rather than suppressed.

The design criteria in Table 23.8 must be selected based on the variables in the first five main columns of the table: piling method, pile height, maximum building height, nominal K-factor, and orientation. The user selects the maximum pile height, which would include the proposed storage height for the facility, and checks to see if the proposed ceiling/roof deck height is within the allowable maximum permitted for that selection. If it is not, a higher ceiling/roof height selection must be made that is within the maximum allowed. The available sprinkler options can then be identified.

Reply
Todd E Wyatt
8/20/2024 08:39:26 am

From NFPA 13-2019's "Enhanced Content" for 21.6 Control Mode Density/Area Sprinkler Protection Criteria for Rack Storage Rubber Tires.

Before deciding to use the protection criteria in Section 21.6, the user must determine whether the storage can be considered miscellaneous tire storage. The definition for miscellaneous tire storage in 3.3.124 differentiates it from any other type of miscellaneous storage:

The storage of rubber tires that is incidental to the main use of the building; storage areas do not exceed 2000 ft2 (185 m2), and on-tread storage piles, regardless of storage method, do not exceed 25 ft (7.6 m) in the direction of the wheel holes. Acceptable storage arrangements include (a) on-floor, on-side storage up to 12 ft (3.7 m) high; (b) on-floor, on-tread storage up to 5 ft (1.5 m) high; (c) double-row or multirow fixed or portable rack storage on-side or on-tread up to 5 ft (1.5 m) high; (d) single-row fixed or portable rack storage on-side or on-tread up to 12 ft (3.7 m) high; and (e) laced tires in racks up to 5 ft (1.5 m) in height.

If the rubber tire storage meets this definition of miscellaneous tire storage, the user should follow 4.3.1.6.

The selection of protection criteria from Table 21.6.1(a) and Table 21.6.1(b) requires identification of the specific tire storage configuration to be protected.

Where the rubber tire storage is being protected with standard spray sprinklers using density/area criteria, the user can use either Table 21.6.1(a) or Table 21.6.1(b) within the bounds of the applicable storage arrangement and storage height permitted by each. Table 21.6.1(b) is referenced in Table 21.6.1(a) for the storage of tires on palletized portable racks and fixed rack storage from 5 ft (1.5 m) to 20 ft (6.1 m) with the tires on-side or on-tread and would be limited to such applications. In most cases, Table 21.6.1(a) and Table 21.6.1(b) provide the user with one density and one area (depending on whether ordinary- or high-temperature sprinklers at the ceiling are used). In some cases, however, the design is required to include a dual design criterion. In a few cases, the user is given some choices of sprinklers only at the ceiling, sprinklers at the ceiling in conjunction with in-rack sprinklers (see Chapter 25), or sprinklers at the ceiling with high-expansion foam.

Reply
Dan Wilder
8/20/2024 09:02:42 am

As to the storage height and clearance, running sprinklers down each row, and offsetting sprinklers between rows to avoid cold solder is one approach. The other is a baffle.

With the open grate mezz, you're looking at a total tire rack storage height above 12'. Have the owner lay down a solid horizontal barrier (either wood above or something under the grating) at the mezz level to split the heights up and get the density requirements down.

If they agree, this gets things down to a EH1, then use High Temp or 11.2K sprinklers for the area reduction to 2,000 FT².


Some discussion on the mezz separation
https://www.meyerfire.com/daily/does-a-mezzanine-change-ceiling-level-density

Reply
Jack G
8/20/2024 06:09:49 pm

oh 2 systems are not permitted for tire storage any more. NFPA 13 2022.
Miscellaneous storage for tires follows NFPA 13. 3.3.131*

Reply
Doug Reed
7/31/2026 11:44:12 am

Why don't NFPA have an ESFR design for tires on side on floor storage over 2000 sf ? Normally 5 ft up to 12 ft. No Racks

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT